I was testing an install that was has just been completed by a chap I work with, quite simple SWA into powder coated IP67 enclosures, that contain some control equipment outdoors.

When I looked he had bent all the banjo's up and connected a flying lead to them, instead of drilling through the box.
Immediately I said you can't do that !!
Now to set the scene this guy is in his 50's and has more qualifications than you shake a stick at.
He said if you drill through the enclosure you will destroy the IP rating, and then asked who said you can't?
Now to be fair I tested one and the Zs was well within.
Just stumped me has anybody else come across this?
I suppose its no different to piranha nuts ?

Before i left I changed them all for Piranha nuts :) Otherwise I won't sleep
 
I was testing an install that was has just been completed by a chap I work with, quite simple SWA into powder coated IP67 enclosures, that contain some control equipment outdoors.

When I looked he had bent all the banjo's up and connected a flying lead to them, instead of drilling through the box.
Immediately I said you can't do that !!
Now to set the scene this guy is in his 50's and has more qualifications than you shake a stick at.
He said if you drill through the enclosure you will destroy the IP rating, and then asked who said you can't?
Now to be fair I tested one and the Zs was well within.
Just stumped me has anybody else come across this?
I suppose its no different to piranha nuts ?

Before i left I changed them all for Piranha nuts :) Otherwise I won't sleep

Nowt rong we that.
 
The banjos can be used inside the box as well in the same manner all linked together and then from last banjo to main earth can't get better earthing than that internal earth and external earthing ie the armouring
 
I suppose that it's just the way I was taught, I would have drilled them all and linked them as well but that must just be me, he did have them bent up in inside, and linked together then one flying lead to the earth terminal.
 
I think your looking into it too deep. If it was a moving part or an exposed part (as in out in the open) then I'd be worried about weakening it. But I can't see any problem with bending it up. I did it today and it doesn't affect the strength of the banjo in any way
 
Bending the banjo's is something I do very often, then linking to the earth point on the cabinet or the next SWA.. Your friend is correct, drilling the powder coating will destory its corrosion proofing. Most metal enclosures have a stud located both on the door and near the top / bottom inside for bonding. Seen it done many a times on different sparks works. Seems to be the norm
 
I was testing an install that was has just been completed by a chap I work with, quite simple SWA into powder coated IP67 enclosures, that contain some control equipment outdoors.

When I looked he had bent all the banjo's up and connected a flying lead to them, instead of drilling through the box.
Immediately I said you can't do that !!
Now to set the scene this guy is in his 50's and has more qualifications than you shake a stick at.
He said if you drill through the enclosure you will destroy the IP rating, and then asked who said you can't?
Now to be fair I tested one and the Zs was well within.
Just stumped me has anybody else come across this?
I suppose its no different to piranha nuts ?

Before i left I changed them all for Piranha nuts :) Otherwise I won't sleep
and has he scaped the powder coat off the area whare the banjo sits?....
 
Bending the banjo's is something I do very often, then linking to the earth point on the cabinet or the next SWA.. Your friend is correct, drilling the powder coating will destory its corrosion proofing. Most metal enclosures have a stud located both on the door and near the top / bottom inside for bonding. Seen it done many a times on different sparks works. Seems to be the norm
all you need to provr here is your R2 is up to the job.....thats what your doing by eartbing the armoured......
 