I was testing an install that was has just been completed by a chap I work with, quite simple SWA into powder coated IP67 enclosures, that contain some control equipment outdoors.
When I looked he had bent all the banjo's up and connected a flying lead to them, instead of drilling through the box.
Immediately I said you can't do that !!
Now to set the scene this guy is in his 50's and has more qualifications than you shake a stick at.
He said if you drill through the enclosure you will destroy the IP rating, and then asked who said you can't?
Now to be fair I tested one and the Zs was well within.
Just stumped me has anybody else come across this?
I suppose its no different to piranha nuts ?
Before i left I changed them all for Piranha nuts
Otherwise I won't sleep