If you had a steel framed building with the electrical service at one end and the gas/water service at the other end. Would it be possible to bond the steel as normal, but then just bond the gas/water service straight to the steel work, instead of taking back to the MET.
 
if you went from the met to the steel then gas then water with out cutting the cable so it was a continuous piece then it would be ok
 
think OP meant could he go from MET to local structural steel, then use that steel to extend bonding t#other end of building, then tap onto gas and water. i think that's a no-no due to the resistance of the steel, possible corrosion, and a few others i can't think of. it's saturday and well past beer o'clock.
 
I believe this is permitted, don't know the regs or any particular conditions which have to be met but when I worked for my old company there was certain occasions when this was done on large steel frame structures.
 
I seem to have read something similar, but it involved the structural steel being used as the means of the earthing (eg. steel being used as a big earth rod.)
 
Extraneous-conductive-part(s) (your buildings steel frame work) may be used as productive conductor(s) providing the conditions of BS7671:2008 Amt 1:2011, 543.2.6 are met. This is quite commonly applied in both commercial and industrial installations, using building structural steel and other extraneous conductive parts too reduce the amount of green/yellow bonding conductor that needs to be run.
 