Can anyone else explain how three MCB's could get fused together like this? And when I say 'fused', I mean even ramming a screwdriver between them couldn't break them apart!
My thoughts are a loose/incorrect connection to the busbar. Mind you, you'd have at least thought they would have tripped long before reaching this state.
Also, note to any of you who come across anything similar, bag it up before it goes in the van otherwise it'll stink to high heaven of the worlds worst and most pungent smell for weeks!
Had exactly the same thing few years ago on Wylex fuses
Like you I couldn't understand why it never tripped and I'm guessing the plastic has melted together
Me thinks you have found the recall MCBs from Wylex / Electrium so buy new ones keep the receipt and then make a claim to Electrium for the £75 payment to change them.
If the load is too high then the CB should have tripped but I would like to look at the bus bar to see if the cb connections to that were really tight and in the right place. mind you I like "Oldtimers" idea best. There could be an internal poor connection in the CB.
it's either a bad termination or a possible recall MCD by electrium. if the latter, get the batch number off the mcb, and then claim through the electrium recall scheme.
Extra-box thinking maybe, but might it have been an extremely low Ze/ super high scc or would that have blown the casing apart?
Shame all of you are all talking about procuct recalls and refunds. I binned the lot a few days ago :( Coulda paid for a few beers :(
I would say it looks like an internal problem. If that was what the recall was about I'm not surprised, they're a fire hazard.
I am surprised you never made the connection as it has been talked about on the forum countless times
I must admit I haven't paid that much attention as of late. 1. I've been too busy, and 2. A massive influx of keyboard warriors recently hasn't inspired much confidence in me to keep active :(
note to self, I must pay more attention! :6:
D Skelton,
sparks1973,