Had a call out this evening to look at a smelly CU.

On the phone I told them to switch off the main isolator which they did.

Arrived and took off the cover to find that the 9.5kw shower was run using 6mm cable which was well and truly knackered and the neutral bar had burnt out.
Also there were a few piggy backed MCB feeding off to other unknown items.
meter tails from head to meter are 16mm. The tails from meter to CU are 10mm.

Going back tomorrow to fit a new CU, 10mm feed to the shower upgrade earthing and new 16mm tails.
 
It was lucky the people were home to notice the CU putting out a bad smell! One of my dad's colleagues, he decided to put his "bargain shower from B & Q" on a 30A BS3036 being run using 4mm cable! It should've been 10mm on 40A. That left some colorful burn marks around the top and bottom parts of the fuse holder!
 
I think you will find the problem was probably a loose neutral, for the amount of time showers are on for they wouldn't do that much damage to a 6mm. In fact on I&T's it is very common to see 9.5kw showers on 40a mcb's run in 6mm2 most seem to present no issues, although depending on the reference method, they do attract a code 2.
 
I think you will find the problem was probably a loose neutral, for the amount of time showers are on for they wouldn't do that much damage to a 6mm. In fact on I&T's it is very common to see 9.5kw showers on 40a mcb's run in 6mm2 most seem to present no issues, although depending on the reference method, they do attract a code 2.

Yeah it was the N Bar shower conductor that was loose (causing the smell and burning) - should have made myself clearer.
The customer had experienced lights flickering for a while so its been on-going.
But also on this job the line conductor has also been getting very hot for a long time and the copper strands have soldered together for as far as I can see the cable before it goes into the wall.
 
Last edited by a moderator:
it sounds like this job was nearly a fire statistic then! its a good job as already posted, that it was noticed! Some CU's are in garages ect, and the customer might not notcice, especially in the winter months.
 
I wouldn't stick a 9.5 on 6mm purely for the fact the cable will be half buried in loft insulation, especially with these loft laggers covering up cables at will.
 