Had a call out this evening to look at a smelly CU.
On the phone I told them to switch off the main isolator which they did.
Arrived and took off the cover to find that the 9.5kw shower was run using 6mm cable which was well and truly knackered and the neutral bar had burnt out.
Also there were a few piggy backed MCB feeding off to other unknown items.
meter tails from head to meter are 16mm. The tails from meter to CU are 10mm.
Going back tomorrow to fit a new CU, 10mm feed to the shower upgrade earthing and new 16mm tails.