Spazz

Just doing a calculation

TT System = 34.97ohms

PFC = 230/34.97 = 0.006kA??? is this right?
 
That's the PEFC is it not?

Max allowable EFLI for 30mA RCD according to Regs 1667 ohms.

Thought it was Power Factor Correction too Tony! Thought we were going to learn something!!
 
Just doing a calculation

TT System = 34.97ohms

PFC = 230/34.97 = 0.006kA??? is this right?

The PFC for a TT installation will undoubtedly be the PSCC value as the PEFC (what you have there) is always much lower due to the high resistance of the earth path.
 