The OP didn't mention that the cut-out was in a zone of the bathroom, if it is then yes a code could be applied, but outside of zones in a cupboard?
 
I wouldn't want it in my bathroom, what happens when I'm really drunk and wee in the sink, and around the sink!!! (I don't really do that!)

Hmm its not a switch or socket outlet, but it must be within the zone around the sink, so its unsuitable for its location. C1 or C2 and it fails anyway.

The dice say C2...

I thought that under the sink wasn't in a zone? I thought it was one of those regs that's seems silly but is true.

I'm sure someone told me once they found a CU under the bath and it was fine because it wasn't technically in a zone although it was extremely bad practice. I may have dreamt this though lol.
 
I thought that under the sink wasn't in a zone? I thought it was one of those regs that's seems silly but is true.

I'm sure someone told me once they found a CU under the bath and it was fine because it wasn't technically in a zone although it was extremely bad practice. I may have dreamt this though lol.

I believe under a bath is zone 1 if accessable without the use of a tool, outside of zones if tool is required, so a hinged door with one pozi screw holding it shut would be fine! lol
 
I believe under a bath is zone 1 if accessable without the use of a tool, outside of zones if tool is required, so a hinged door with one pozi screw holding it shut would be fine! lol

Yeah that's what I thought because he said something about it needing a screwdriver to open the panel of the bath but at the same time that's a pain if you have an mcb trip out lol
 
Yeah that's what I thought because he said something about it needing a screwdriver to open the panel of the bath but at the same time that's a pain if you have an mcb trip out lol

Not a problem if you have a wylex rewireable, fuses never go!
 
check length of tails from meter to incomer..be sure to check DNO for max length (unprotected)...if length over....then C3 it........as all it needs is improvement...
 
The EAWR99 applies everywhere where electricity is used.

Everyone has a duty of care over themselves and everyone who is in the area (including a home if a visitor comes in)

Whoa back there nick ..................it most certainly does not cover a non working environment.

It does if your building the house, and rewiring it, or even just working on an existing circuit, but I hate to think that every householder in the land will have to carry out risk assessments, method statements etc to live in one
 
The maximum length for unprotected conductors is 3m as per Regulations 433.2.2 and 434.2.1.
Reality goes out the window here, as although the DNO fuse may well be rated so as it will provide protection for tails that are longer than 3m, if they decide their device their device isn't to be used for that purpose, then the tails are considered as being unprotected.
Whilst the majority allow 3m, some will only allow 2m and some will allow 4m.
Then of course you get variations depending upon who at a particular DNO you speak to.
To my mind, the main problem with the OP's scenario, is the lack of RCD protection.
Whilst the DNO fuse may well be outside of any zones, the supply to the fuse and the distribution circuit to the Consumer Unit are in a location containing a bath or shower, and will still be in that location even if boxed in and only accessible by use of a tool.
Of course, on the other hand, the supply and the fuse are outside of the scope of BS7671.
As such the requirements of BS7671 for additional protection by means of a 30mA RCD do not apply.
 
Spin would you say that there is a change of circumstances on those tails that would invoke the regs.

I suppose if they are coming out of the Head under the sink in say 16mm for argument sake and go through the wall into this cupboard and then into the meter then yes you would have a change in erection methods, but those would be the DNO tails and not come under specs.

if the meter is also under the sink and they go through the wall from the meter into the CU cupboard then yes I would agree that you need to go by the regs there.
 
This is it Malcolm.
Where does BS7671 kick in, and if the DNO fuse is providing protection for the tails what Regulation in BS7671 is not being complied with?
 
This is it Malcolm.
Where does BS7671 kick in, and if the DNO fuse is providing protection for the tails what Regulation in BS7671 is not being complied with?

Who owns, supplies, fits the tails from the C.U to meter,, the property owner or his agent.
Who owns the meter,, not the property owner.

It must start at the meter end of the tails, to include those tails.

Unless meters are mentioned in BS7671 then the meter and it's tails are also covered.
 
Meters are not actually mentioned in BS7671, although the distributers equipment is mentioned and it's condition and rating should be assessed to ensure that it is adequate before conducting an addition or alteration.
However a periodic inspection may not necessarily be being conducted in preperation to making an addition or alteration, and as such there is not always a requirement to assess the condition of the distributor's equipment.
Then of course, there is the problem, that although the tails from the meter are generally considered as being part of the installation, and not part of the distributor's equipment, there is generally no access to the meter terminals.
It's a requirement when conducting an inspection that we check the connection of conductors.
This obviously presents a slight dilema.
If the tails being conductors are considered as being part of the installation, we are required to check their connections, yet we are prevented access to those connections at the meter.
The meter being part of the distributor's equipment.
It doesn't seem to matter who supplies the equipment.
In many cases the installer/customer is required to supply a meter cupboard, thich the DNO seems to think is their property and will often not allow any other equipment other than theirs to be installed in such a cupboard.
 