R
RogertheBodger
Hi Guys and Gals.
Working in a large garden today, lots of lighting, several sets of ground mounted 1W Led's,not installed by me but all worked good for a couple of years to my certain knowledge.
Today, one set of six are not working, they are all wired back individually to a central point where they are supplied by a 3-38v 350mA driver. disconnected the output side and tested it - 0 volts, OK fine.
fitted working driver from another set, output from this driver is 39v DC but lights still not working sounds to me like all six are goosed, can't see one volt over the driver rating being enough to take them all out?
Sooooo, cause? .................... I'm imagining the gardener hitting a cable run, dead shorting it, and the spike has gone through the driver somehow and out to the lights, overloading them, can't say I know a lot about Led's, spent an hour looking at this on the net and they don't seem to be the type of lights that take what current they need, rather the type that only work on the current they're given and as such can be easily overloaded, can't understand why all six should go at the same time, so any thoughts, as always, gratefully received.
I maybe wrong but i think the driver will only show output under load ?:grinningelf::grinningelf::grinningelf:
Edit ; Sorry Rodger i could not help it ! :35:
some of the older LED lights had a in and out on them and if 1 LED failed that used to stop the rest from working ( a bit like the oldish Xmas tree lights one core going to the lamp then onto the next and then finally a single core back)
With out seeing them i can only guess
I would be inclined if its possible to remove one of the faulty LED and add it to the set that are working
Good luck
Good luck
Thanks Ashrow, I know the ones you mean, but these are connected to the driver in parrallel, I've connected them one at a time to a good driver from another set and nothing,
so I'm pretty sure they are busted but don't know why.
perhaps a fault on the driver spiked to a voltage over the LED rated supply before the driver failed ?
I was thinking along those lines, I'm wondering now what the individual voltage per led should be, they all got 38v DC and worked OK, or if they should be connected in series, it's a head scratcher.
The more I read about Led technology the more complicated it gets!
There are two main types of LED driver, constant voltage and constant current.
Constant voltage for lights in parallel and constant current for lights in series.
Hi Ackbar.
The drivers in use are constant current, so you are suggesting that the led's have been connected incorrectly all along? even though they have been working correctly for a couple of years, and that the excess voltage has done them in eventually?(but all at once?) wish I knew what the voltage was supposed to be! but that is certainly something to think about.
Not necessarily, Usually you need a power driver for each series string of LEDs but you can, with some devices have more than one string in parallel
The advantage of using a current drivers are length of run up to 150m and low voltage, anywhere between 100mV -16V, very small conductors <1.0mm2.
If the lights were wired entirely in parallel then it must be a Voltage operated device. Although having said that there all sorts of variations of design. You will need to look at the specific manufacturer's information
RogertheBodger,
ackbarthestar,