ezzzekiel

anyone have an opinion on this statement:

Main Bonding is there to protect you. A fault current will always try to find a path down to earth, literally to the ground. The current will always take the easiest path to ground; the idea of Main Bonding (and Supplementary Bonding) is to create an alternative path for the current to flow that is an easier path than along one of your heating pipes, along your arm, through your body, down your legs to the wet kitchen floor and to ground. By using a thick copper cable, you are creating a path that is more inviting to any fault currents and will divert any fault currents from your body or places where it should not go, as the current flows down to ground
 
seems to describe earthing

main bonding to me raises the potential of extraneous metalwork to that of exposed metalwork in a fault scenario
 
Bonding and supplementary bonding are also separate things, bonding will provide a path to earth but supplementary bonding is achieved by creating a zone of equipotential voltage and is not connected to earth. If everything in that zone is at the same voltage then there is no chance of getting a shock. He or she in this statement is using terms like bonding but describing earth fault path.
 
maybe just me being picky, but nephew doing an electrical course at college and this info was gathered from the internet, on looking ive found it on the front page of a few electrical firm websites, maybe theyre just simpliying it for the home user.
 
it does try and explain in laymans terms what bonding does to joe public.
just falls down a bit on the science.
 
supplementary bonding is achieved by creating a zone of equipotential voltage and is not connected to earth.
it connects to earth via all electrical equipment within the location that is supplentary bonded
 
Yes, if they are trying to tell people bonding is there for there protection and separating it from the cpc or earth in there supply cable that protects the circuit, its basic but correct. If you wont to understand the difference between earthing, bonding and equipotential bonding then start by looking up the definitions of those terms in the big green book BS 7671. if he is on a course he'll probably have one.
 
If you want to understand the difference between earthing, bonding and equipotential bonding then start by looking up the definitions of those terms in the big green book BS 7671.

thanks i will start there, what is the big green book
 
Bonding and supplementary bonding are also separate things,
Not really.

bonding will provide a path to earth
Main Bonding is applied to equalise potential on extraneous conductive parts which are already earthed (by the ground).

Supplementary Bonding does the same on a local basis (in a location).
 
Sorry meant to say not related to earth, as in they are different issues. The green book is The Requirements for Electrical Installations BS 7671.
 
Not really.


Main Bonding is applied to equalise potential on extraneous conductive parts which are already earthed (by the ground).

Supplementary Bonding does the same on a local basis (in a location).

Earthing and Bonding are 2 different things and offer 2 forms of protection (formerly refered to as EEBADS).
Earthing is the creation of a low impedance path (Zs) back to the star point of the supply transformer which should cause Automatic Disconnection under earth fault conditions so long as the circuit is designed and installed correctly.

Bonding is the creation of an Equipotential Zone (Faraday Cage) so if one conductive part becomes live under fault conditions all other exposed/extraneous conductive parts rise to pretty much the same potential. If touch voltages between simultaneously accessible parts is kept down to below 50v then this should protect against fatal shock.
 
I wasn't talking about earthing.

I was replying to the statement that main and supplementary bonding were separate things.
 
you are right of course that is what i put, wonted to make a distinction between earthing and bonding and wrote bonding and bonding. my only excuse is being a dyslexic and not everything that is in my head comes out on the page. but I should have spent more time checking what I had put down before i hit send, makes me look stupid and is frustrating when I really wont to take part in these debates. My apologies.
 