I have been asked to carry out a rewire of a top floor flat when checking the existing supply characteristics.
TN-S with a ZE of 1.24 ohms and PFC of 1.91 KA. 1361 Type 2 with 100 amp Fuse

Should I contact the DNO and ask for them to come and check before commencing work.
Unable to treat as TT and run earth cable down the back of the building, will be using a Wylex dual RCD board for all circuits.
If I complete a certificate all my Zs reading will be really high.
 
Yes that ze is far too high, should be about 0.8 for a tns system. Contact dno and ask if a tncs upgrade is available, otherwise no choice but to convert to tt.
Could be that the dno have not provided an earth for that installation.
 
Last edited:
Sounds to me like a tester issue because if the supply voltage is 240v and PFC is 1910a then Ze should be about 0.12ohms I think
 
  • Like
Reactions: 4 people
Nulled the leads, using a Megger 1653 used on the next job all readings good. Going to contact DNO tomorrow and ask them to check.
 
Think you NEED to answer Jeremy's question first, BEFORE you go calling the DNO!!!


Is the origin of the supply in the flat or in a communal meter cupboard downstairs?

The way i'm reading your OP, is that your taking your Ze test readings from the flat's CU which isn't Ze at all, but Zs, and you should be leaving all earthing and bonding conductors in place for a true Zs reading. Taking Zs at the sub-main CU, is commonly called Zdb...
 
Last edited by a moderator:
  • Like
Reactions: 3 people
Also remember to disconnect the main earth ( if possible too) and also remove the loads on the installation
 
and whare did `you will have to TT it` come into this eh?....its a distributers earthing facility......so they have to maintain it.....
 
contatced DNO they are comming out on Wednesday this week to check all the flats are due for an upgrade.
See what they say let you know thanks for all input.
 
Just a POINT with the Ze. Looks like you're getting the right figures, not necessarily in the right order.
 
Last edited:
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
High ZE Reading in Flat
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
27

Advert

Thread statistics

Created
jengo22,
Last reply from
Amp David,
Replies
27
Views
5,825

Advert