i've installed it using the steel frame and i've seen countless steel frame factories new and old wired the same way.
 
Been doing this for 28 years on large construction sites gas and water still bonded so i am not naive but you obviously think you know it all lol
 
If you had a steel framed building with the electrical service at one end and the gas/water service at the other end. Would it be possible to bond the steel as normal, but then just bond the gas/water service straight to the steel work, instead of taking back to the MET.
Yes that would be acceptable.
 
Been doing this for 28 years on large construction sites gas and water still bonded so i am not naive but you obviously think you know it all lol


Well i obviously know a bit more than you after your 28 years!!

Perhaps you can explain why you would pull a separate bonding conductor over several tens of metres of a steel framed building, rather than using the mass of steelwork that's already bonded to the MET??
 
I agree, use the steel as a bonding conductor. If you fancy, you could use it as a common CPC too!
 