Just went to do a pre CU change check on a house on TT.
It didn't start well when a quick Ze test got 1540R and that was with the bonding still in place!
After abandoning my checks and digging up their patio I found this.....

After a temporary fix with a choc block the Ze had gone up to >2000R! It turns out there was yet another break in the cable so the only "earth" was this nut and bolt 6 inches down in gravel.
The scary thing is that this was under paving slabs, at least 20 years old I reckon- I suspect the cable was probably sliced multiple times when the slabs were fitted and only one joint "repaired".
So the house was almost certainly without any sort of earth for 20 years plus!
It now has a new spike banged in and a much more healthy Ze. Plus instructions to the owner to fit the earth pit properly before I go back unless he wants my bill to go up significantly :lol: