R
rob.allen3000
Can anyone help? Is a metal kitchen sink considered a extraneous conductive part when it's fed by plastic pipes?
not normally unless it's got metal waste . acid test is to IR test from sink to MET. if it reads >22kΩ, then you don't class it as extranoeus.
^^^^^ as above, though it's amazing how many Clerks of Works particularly in Councils etc who still look for a bond to metal sink units no matter the circumstances....and won't be told otherwise!
One of the problems and a major cause of confusion to those that don't know the criteria for bonding requirements. Is that most manufacturers of stainless steel sinks and commercial stainless steel tables and the like, STILL provide a marked designated bonding point!!!
e54, that's to connect the earth rod to. :behead:
The only circumstance in which I can see a metal sink being an ECP is if it is fixed to structural steel work within the fabric of the building.
If supplied by metallic pipes or wastes it will be the pipes/wastes that are ECP's NOT the sink.
but if the metal sink has electrical conductivity to the metal waste, then the sink itself becomes extraneous.
it's a phenomenon called idle-itis, very common in the under 25's. biff.
rob.allen3000,
Engineer54,