BrianDB9

I'm tending to favour an approach of time to start smelling the coffee at 30 and start saving / planning and rewire at first convenient oppurtunity but don't let domestic wiring get over 40 (for management purposes)
I realise that you can test and still say wiring is "ok" for a lot longer than that and other factors kick in eg sparse provision of sockets leading to overloading etc just wondered what the general feeling was ?
 
If it's wired in PVC,it's still in good condition,circuits are correctly installed and all circuits have cpc's why rewire?.....I work in plenty of properties with imperial wiring 40 years old which will probably go on for another 40 with the usual updates to circuit protection etc.
Only time I would automatically condemn is rubber/vir or lead.....there arent many of those left now thankfully......oh and pre-70's lighting circuits with no cpc's unless there is no likelyhood of class 1 fittings.
 
This is a joke thread isn't it? Maybe we should suggest a rewire instead of respecting. Change the stickers from next inspection date to rewire due date. Should a 1920 Rolls Royce be taken off the road because it doesn't have ABS, satnav or air bags?
 
Just rewired my house! Wiring was 50 years old, aluminium conductors throughout and no cpc's in lighting.
 
One problem with older installations is there is often not enough points/in the wrong place.

I recently rewired a ring final cct on a 25/30 year old installation just because there wasn't much difference in price between adding extra sockets to the existing, and carrying out a rewire.

I worked for a local authority who deem 30 years as the end of an installations life. I didn't always agree with it, but it was their policy.
 
One problem with older installations is there is often not enough points/in the wrong place.

I recently rewired a ring final cct on a 25/30 year old installation just because there wasn't much difference in price between adding extra sockets to the existing, and carrying out a rewire.

I worked for a local authority who deem 30 years as the end of an installations life. I didn't always agree with it, but it was their policy.
The 30 year figure is based on a job that comprises of conduit and VIR cable that could be easly rewired without much disruption as it was felt that the cabled would dry out and break down now its down to the environment the cable is run in and at the end of the day it down to testing if its fine then it is servicable
 
The 30 year figure is based on a job that comprises of conduit and VIR cable that could be easly rewired without much disruption as it was felt that the cabled would dry out and break down now its down to the environment the cable is run in and at the end of the day it down to testing if its fine then it is servicable

Agree, ...the only thing i would add is ''Inspection'' & Testing'', the inspection for obvious reasons...
 
Just to add this theory was based on a Government building I know this because I served my time on the government term contract with Mathew Halls and we had the job in the late 70,s early 80,s to rewire a lot of building mostly in conduit or micc
 
Just to add this theory was based on a Government building I know this because I served my time on the government term contract with Mathew Halls and we had the job in the late 70,s early 80,s to rewire a lot of building mostly in conduit or micc

Now those were the day's when things were done properly!! lol!!
 
i dont go by age unless visible decay or heat damage is present. (except for old rubber insulation)
I rely on insulation testing with a good megger
if even questionable readings occur i replace the wire immediately
 
This is a joke thread isn't it? Maybe we should suggest a rewire instead of respecting. Change the stickers from next inspection date to rewire due date. Should a 1920 Rolls Royce be taken off the road because it doesn't have ABS, satnav or air bags?

I would suggest considering whether generally speaking installations above 30 have adequate provision of sockets that promote safety by way of reducing use of extension leads, adaptors, and therefore indirectly slips trips and falls / risk of Fire etc.

It would be embarrassing if you just passed an installation off as ok with one single unswitched socket per bedroom and the fire service did an advice visit and suggested overloading.
I dont think the occupier is going to feel they were professionally advised ?

Do you consider who is likely to be living in the property - bungalow is likely to be elderley or disabled does that affect your professional judgement ?

I also consider the installation from the customers point of view - if an electrician tells me its fine and i move in, and spend all my savings decorating then find major repairs are needed causing me to take time off work, maybe i'm not going to spread the good word about the advice given ?

Electrical safety shouldn't be treated as a joke ? but thats only my professional opinion.
 
Brian please don't hide behind electrical safety yes it is not a joke but if you are going to be "professional" about it you have to understand that you cannot insist on a rewire because you do not think there is enough socket outlet . If the installation passes all the tests then its good to go now you may want to suggest the customer get RCD protection or more socket outlets instead of using leads fine but you cannot condem an installation on these grounds as the customer could take legal action on you or your company for forcing them to have work done that was not necessary.

Remember we as electricians do have the same rights as the gas guys were we cannot isolate anything without the customers consent also you are on dangerous ground if you try and impliment change on the grounds of your interpitattion of electrical safety. Yes I know we could have a better system but these are the regulations that we must comply with
 
if it passes the inspect and test, then fine. BUT, i always give my personal opinion. If i wouldnt be happy with it in my house, then i say so. Surly even though its ok by the book, your personal HONEST opinion stands some bearing. They may act on it, they may not.
 
I remember when I moved into my current house about ten years ago, there were 4 sockets in the whole house all on one circuit, one in the living room, one in the kitchen, one in the cellar and one in the first bedroom. The two bedrooms on the top floor had no sockets at all, the previous owner used to have an extension lead running up the stairs. One of the first jobs I did was change CU and add more circuits and obviously sockets. The old installation tested fine though....only reason I rewired was for practical reasons. I left the lighting circuits as they tested fine and at the time had other things to spend my time and dosh on.
 
So the NatWest tower now needs a rewire because it's over 30 years since completion and there's a possibility of there not being enough sockets and people in there using "GASP" extension leads.

Oh, hang on, it's probably only houses you're talking about.

cba with this or most of the other threads at the moment and for that reason, once again, I'm out.
 
Brian please don't hide behind electrical safety yes it is not a joke but if you are going to be "professional" about it you have to understand that you cannot insist on a rewire because you do not think there is enough socket outlet . If the installation passes all the tests then its good to go now you may want to suggest the customer get RCD protection or more socket outlets instead of using leads fine but you cannot condem an installation on these grounds as the customer could take legal action on you or your company for forcing them to have work done that was not necessary.

Remember we as electricians do have the same rights as the gas guys were we cannot isolate anything without the customers consent also you are on dangerous ground if you try and impliment change on the grounds of your interpitattion of electrical safety. Yes I know we could have a better system but these are the regulations that we must comply with

Thats right oldtimer but we are professional and also human hopefully we can go beyond mere regulations that are only regulations and not law and advise customers of other aspects that electrical work has an impact on, eg I would consider just a board upgrade and enhanced smoke detection where a tenant was frail and a management rewire would cause more harm than good.

I would question if it is good customer service to carry out an EICR or similar and just hand it to a householder (who can not understand them ) and just say "its good to go" is that really what they expect ? Its like going to the doctors and they say your hearts beating and your breathing everything is fine !
 
So the NatWest tower now needs a rewire because it's over 30 years since completion and there's a possibility of there not being enough sockets and people in there using "GASP" extension leads.

Oh, hang on, it's probably only houses you're talking about.

cba with this or most of the other threads at the moment and for that reason, once again, I'm out.

The management of the nat west tower who ask for it testing would be well advised to consider those aspects yes ! Closed mind methinks
 
Brian I agree that we have regulations and not laws we also have a lawyer culture in this country and a mentality that says hold on I can sue this guy via a no win no fee lawyer. Also you may recommend to the customer to upgrade the installation but if the tests are ok you cannot insist they rewire it.

I did a job for someone who said that their friend had their property failed for not having RCD protection so they got another spark to replace the fuseboard will I have to do the same I said no because if your installation passes the relevant tests then fine but if you are modifying or updating the installation then yes RCD protection may be required. Fine I got a call a week later to tell me her friend had sent the bill for the new consumer unit to the guy who tested the property stating if he did not pay it she would pass the case on to her lawyer. Never found out the outcome but I hope he did have to pay because we are here to supply a service not to extort money out of people under false pretenses under the pretense that we are doing it for their health and safety
 
once an installation passes the tests then all you can do is make recommendations E.G if it was me I'd have a new board with rcd protection,but you cannot force someone to take your advice as it is just advice,also personal preference plays its part,you may prefer to upgrade your system to rcd/mcb the customer may not just like you may prefer not to adopt some of the hideous decorating schemes that we see,its all about personal preference.However if you start using scare tactics to frighten someone into having work done then your on your way to a spot on rogue traders.At the end of the day you do your tests issue your report and give advice where needed,after that it sup to the client but remember being pushy can cost you work.
 
How about green goo? I've come across it a few times recently & have a property to test that suffers from this phenomena. Apparently it does not have a detrimental effect on cable but isn't particularly pleasant especially if it's oozing from your sockets. Cables that suffer from this were installed late 60s early 70s by all accounts making them approx 50 years old, well beyond the suggested 30yrs but if they tested ok, hmmm. Will be interesting to see what sort of test results I get. I think if it was my house & I could afford it I'd have it rewired regardless, anybody got any thoughts on this?
 
How about green goo? I've come across it a few times recently & have a property to test that suffers from this phenomena. Apparently it does not have a detrimental effect on cable but isn't particularly pleasant especially if it's oozing from your sockets. Cables that suffer from this were installed late 60s early 70s by all accounts making them approx 50 years old, well beyond the suggested 30yrs but if they tested ok, hmmm. Will be interesting to see what sort of test results I get. I think if it was my house & I could afford it I'd have it rewired regardless, anybody got any thoughts on this?

Search : Electrical Safety Council

type in 'green goo' and open the link to 'switched on' issue 19
 
if its been wired 50 years ago by an electrician, not botched by DIY, cables, accesories and terminations are in a good condition, I would only add an RCD on incoming tails :)
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Rewires - what age do you suggest it and is there an age you condemn at ?
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
24

Thread Tags

Advert

Thread statistics

Created
BrianDB9,
Last reply from
amlu,
Replies
24
Views
3,761

Advert

Back
Top