What problems, if any, do you see with this neutral setup...


L1, L2, L3 supplies taken from a large 3ph DB on 3 seperate 16A MCB's and 3 seperate 4mm cables, they enter into a contactor housing at high level. L1, L2, L3 switched by the contactor after which they go to 3 seperate discharge lighting cicuits. The neutrals of all 3 circuits are connected together in the contactor housing (Connector block). Similiar but not identical loads.
 
Work it out you're self
In=√((Ia²+Ib²+Ic²)-((Ia*Ib)+(Ia*Ic)+(Ib*Ic)))

Tony, I know you own this electrical knowledge, but could you entertain and enlighten the stupid (me) and expand a little on this. I had a ****s poor apprenticeship but am always looking to become better informed.

Thanks.
 
I own no knowledge. The formula can be found by looking.

RE the harmonic neutral current, without a power quallity meter or the data given by the lamp manufacturer it's near imposible to calculate.
 
What problems, if any, do you see with this neutral setup...


L1, L2, L3 supplies taken from a large 3ph DB on 3 seperate 16A MCB's and 3 seperate 4mm cables, they enter into a contactor housing at high level. L1, L2, L3 switched by the contactor after which they go to 3 seperate discharge lighting cicuits. The neutrals of all 3 circuits are connected together in the contactor housing (Connector block). Similiar but not identical loads.

What's the reason you don't use 3 double pole contactors and do the job properly.
 
Work it out you're self
In=√((Ia²+Ib²+Ic²)-((Ia*Ib)+(Ia*Ic)+(Ib*Ic)))

The loads are unknown, I guessed at L1-10, L2-9, L3-11 and got 1.73A (That correct?). The loads may differ more, this is to settle a bit of a debate. Im geussing tony that because one neutral could handle the total neutral current then that aspect of it is ok?...

There was more to this debate though.
 