Hello people
Can any provide me a basic drawing of a contactor connected up does the neutrals have to go in supply side of contactor or can they all go on neutral back and a link from there to a2
 
google it . loads of drawings on the internet.
 
A contactor is really a set of contacts...normally 3 or 4 operated by an electromagnet...how it's connected depends on what it is operating.
 
So lets say its a 24a 4 pole contactor i could use 3 poles for the live conductors and the 4th pole neutral conductors the a link from neutral to coil
 
Treat the contractor like everything else in our world. It's a switch.
you have A1 and A2 which is your coil contacts. And usually you have 1,3 and 5 which is your "feed" at the top of your contactor and 2,4 and 6 which is your "load" at the bottom. Your A1 is usually your live of your control and A2 your neutral.
It all depends on what your using it for, and location etc as to how you wire it.
Fr example if your wanting to switch a bank of lights and they are controlled via a local photocell, the photocell would be wired via A1 and A2 so when the photocell closes (as its just a switch like everything else) it will send voltage to the coil energising it and pulling in the contacts allowing your lights to switch on.
If you have 3 separate circuits you want to switch then you will have 3 breakers controlling your lights and a control circuit controlling the photocell.

You get lots of different types of contractors so make sure and get the right one for the job, ie normally closed/ normally open/ coil voltage is it dc/ac etc
but as everyone has already said, pop the search in to google and look for images. It's basic wiring and fairly straight forward.
 
Yea I had this debate with an old colleague a few years ago with regards to common neutrals. And that taught me a lot about contractors as I did plenty research in to how they worked etc to prove a point!
Best advice would be to swat up and learn how things work. It makes life so easier for the future if you understand why things happen.
Some contractors have a designated connection for neutrals and its not switched so just like fancy connector block!
nowadays you can get almost anything you want when it comes to electrical components/switches/
 
Make sure you get the correct one for the loads, some may have 4 poles but 3 are load carrying and the 4th is an auxilliary (lower rated) contact.
 