Work it out you're self
In=√((Ia²+Ib²+Ic²)-((Ia*Ib)+(Ia*Ic)+(Ib*Ic)))

There is a simpler version of working out In, but I can't be bothered working it out.
Brain isn't working today and I might get it wrong!


If there isn't a Neutral back to the supply, that's where it starts getting interesting!
(as readers of another location will know :wink_smile:)
 
Last edited by a moderator:
The loads are unknown, I guessed at L1-10, L2-9, L3-11 and got 1.73A (That correct?). The loads may differ more, this is to settle a bit of a debate. Im geussing tony that because one neutral could handle the total neutral current then that aspect of it is ok?...

There was more to this debate though.

Spot on.

I Wrote an Excel spreadsheet for electrical calculations. PM you're e-mail address and I'll send you a copy.
 
is that not like borrowing a neutral , if someone was checking a fault on the dead circuit and disconnected the neutral it would become live if the other 2 rows were switch on , is this right?
 
is that not like borrowing a neutral , if someone was checking a fault on the dead circuit and disconnected the neutral it would become live if the other 2 rows were switch on , is this right?

No as the other 2 neutrals would still be connected...
 
I thought he was joining the neutrals up on the contactor enclosure then running a single neutral to the board?
I.e the reason for asking about neutral current?


No, there just linked together in the contactor enclosure. The reason the neutral current was mentioned was if a neutral was lost it could go undiscovered as the circuit will still work as the other 2 neutrals will carry the current. Although unlikely the other neutral could also be lost and the circuit would still work with the last neutral carrying the 3 circuits neutral current.

Also im the OP, this setup is already in use, we're looking at adding to it. I had a discussion with another spark and had very varied views on it. So thought id cast the net wider and see other opinions. There's no real issue in seperating the neutrals, just a sort of theoretical discussion on it.
 
No, there just linked together in the contactor enclosure. The reason the neutral current was mentioned was if a neutral was lost it could go undiscovered as the circuit will still work as the other 2 neutrals will carry the current. Although unlikely the other neutral could also be lost and the circuit would still work with the last neutral carrying the 3 circuits neutral current.

Also im the OP, this setup is already in use, we're looking at adding to it. I had a discussion with another spark and had very varied views on it. So thought id cast the net wider and see other opinions. There's no real issue in seperating the neutrals, just a sort of theoretical discussion on it.

if theres 3 circuits fed into the contactor enclosure then there needs to be 3 neutrals.
dont see where the confusion is lol.
 
bad practice to use 3 single mcbs on 3 different phases into the same enclosure , in my opinion
 