You cant put in a triple pole mcb, It's not a 3 phase circuit, it's 3 single phase circuits on different phases with a borrowed neutral condition at present, so you would need separate neutrals for each circuit and switch the phase conductors through the contactor
 
The way I read it earlier there is no neutral back to the board at all, only the 3 returns from the lighting circuits joined together and going nowhere.

If it is a single neutral to the board then it's a 3 phase circuit, but it's still not a 3 phase contactor.
 
it is 3 phase if he is using the 3 phases and only one neutral in my opinion
He's only using the contactor to switch 3x individual lighting circuits, it doesn't say the contactor is 3phase, and there is no 3phase load so how can it be a 3 phase circuit??

it should be wired as 3x individual 16 amp lighting circuits with a neutral for each
 