Hi there,
I recently completed a PAT Course and have been working on increasing my experience testing various kinds of equipment. I have a lot of questions around how to test expensive audio engineering equipment appropriately.
Thankful to have found this forum!
 
Welcome to the forum.

Expensive audio engineering stuff?! That sounds interesting what kind of things does that include?
 
Welcome to the forum.

Expensive audio engineering stuff?! That sounds interesting what kind of things does that include?
Hi there thanks for the welcome!

Well the toughest ones are the L'Acoustics 12x (4x as well) Amplifiers. They power speaker systems for large festival events. But when I spoke to some folks who regularly do PAT testing they said that I would need to be very careful not do run 500v cause I could break them so to do a soft test instead (which makes sense). But then someone else said if I do the power on test at all even with less power that it will break the equipment because they can't be partially turned on without receiving the full amount of power required without also causing damage to the equipment.

I have the opportunity to test quite a few of these items but they are worth multiple thousands of pounds so I'm very concerned about just "giving it a go" without knowing exactly how to test them properly. But everywhere I turn I can't seem to get a straight answer. In the end I was advised to only conduct a visual inspection on anything I wasn't comfortable testing on jobs I'm working on, but surely if I'm being asked to complete a PAT testing job I should be able to PAT test all the equipment on that site.

Would so appreciate any wisdom this forum might have on the topic. I'm also happy to move this question to the PAT testing thread if that makes more sense.
 
500v shouldn't do any damage to a 230v appliance. Your tester should connect live and neutral together for the test however if it incorporates filters you will get odd readings and will have to revert to 250v. Not sure what you mean by the power test.
 
Thread moved to Pat testing. Thread title changed to how to test expensive audio engineering equipment appropriately, to suit the topic.

Thread moved mate. Im not a spark myself so wont attempt to answer that. But would love see a pic of these beasts!
 
So basically as I understand it, the L'Acoustics Amplifiers are technically Class I and research suggests that I would need to use a soft insulation test at 250V instead of 500V to avoid damaging the sensitive surge-protection components. But then when I mentioned the test to someone who has been in the production industry (not a pat tester but years of electrical and practical knowledge within the industry) he sort of said that any warehouse he worked in would never have done that kind of test on an Amplifier and that it would undoubtedly damage the amp. So that has made me hesitate. Another person with a lot of PAT testing experience mentioned that the really problem is not sending 250V to the amplifier but the fact that it is a short burst of power. Basically they were saying that because it's a short burst of 250V the amplifier isn't able to fully complete the start up process and only half turns on which can (in their opinion) damage the inner circuitry. So I just feel like I'm caught between a rock and a hard place not wanting to damage this expensive but of kit but also feel like I should be able to complete a test of some sort on it. I just would love to chat with someone who has practical experience PAT/Electrical testing this kind of gear so I could know what the standard process is.
 
as westward says, the L and N are connected during test, so there will be no voltage able to start the equipment up.

The whole point of PAT is to ensure its safe..... other words, making sure no serious voltage is present on the metal casing where someone might touch it

so L+N together, measured against E


A PAT only tests the SAFETY of equipment, not whether that equipment operates correctly
 
I will try and research this further over the weekend, and again apologies for my lack of experience in this area, but at least when I had looked at it a month ago it seemed to suggest that because of the design of the switches and the surge protector on the amplifier I would need to run a Touch Current Test. This is the test I'm referring to that powers on the equipment for a short time. I think it's something to do with the fact that a regular Class I test alone will not adequately test the amplifier accurately.
 
THe model of tester can make a difference. I know the Seaward Supernova does power the item up during a standard test. Thia can be edited out on a custom test though.
 
I will try and research this further over the weekend, and again apologies for my lack of experience in this area, but at least when I had looked at it a month ago it seemed to suggest that because of the design of the switches and the surge protector on the amplifier I would need to run a Touch Current Test. This is the test I'm referring to that powers on the equipment for a short time. I think it's something to do with the fact that a regular Class I test alone will not adequately test the amplifier accurately.
Having looked at the manual for the 12kW amplifier, I think you are right that the unit would need to be powered up in order to do a Protective Conductor current test. Doing a test without turning it on won't provide a connection to the PSU etc. The amp apparently has a 6 second start-up cycle!
You would ideally need a tester that does a proper Protective Conductor current test by measuring current in the earth wire at the plug when the unit is powered at 240V.

I think your best bet would be to try to talk to L'acoustics - they have an office in London, or you could try their technical enquiry service, though PAT testing is not a thing in France as far as I'm aware!

There may be precautions needed such as connecting dummy loads to speaker outputs, but I suspect the amps are so sophisticated they would be protected internally from harm.
I would say the advice you had about not applying anything higher than mains voltage is sound. Other advice suggesting that merely turning the equipment on will cause harm, I think is exaggerated, but check with the manufacturer.

The migration from IR measurement to earth leakage current is touched on here : Earth Leakage Tests in PAT Testing - https://pat-testing-expert.com/advice-hub/leakage-tests

I know it's not "PAT" any more, but old habits etc.......🤪
 