DJM Sparks
Fella's, thanks for the advice,much appreciated, gonna swerve the diggin myself------------looks like the old mans getting wheeled out for this one!!!!
Hi all,
I am pricing for providing 2 x 16a radial circuits for elec gates, one thing I am a bit stuck on is the acceptable deptch for the supply cable. I know there isn't a standard depth however I was airing on the side of caution and will propably go for and SWA within ducting with danger tape over the top at about 300mm depth.
I am going way over the top or can anyone add their views?
Cheers
Dan
You can never be too careful when it comes to electrics mate, what you're doing sounds fine to me!:D
Hi all,
Cheers
Dan
Hi are you referring to the depth in the ground? if so i was always told about 18 inches :)457.2mm
the minimum depth is actually 500mm deep with the tape at 150mm below the surface. hope this helps
Hi, As a general rule Buried cables should be a minimum of 500mm with marker tape 150mm below the surface. 522.8.10 from red book states you can use conduit, duct or SWA or all of them as long as there is mechanical protection.
600mm is in areas of agricultural premises and caravan locations where vehicles and Mobile machines are operated,
I have always been told to install it at 600mm.
Hi all,
Cheers
Dan
Get yer shovel out again then