is posting on old threads frowned upon then? I ask out of genuine curiosity as I haven't heard that one yet??

atb
 
is posting on old threads frowned upon then? I ask out of genuine curiosity as I haven't heard that one yet??

atb
usually if the new post is meNINGLESS OR IT'S TO BOOST A POSTER'S POST COUNT.
 
There is NO " magic number " of mA that can be fatal, everybody on here seems to have their own figure. Every body has it,s own tolerance to electric shock, therefore the boffins have decreed 30 mA is a safe protection. It,s the energy that can kill....power X time.
 
I like this thread also its a funny thing as i watched a program, where a Test Dummy was in a bath and he died every time above 6mA or was it 6ms, LoL it was one of them, Age I suppose still maybe one member here could find out truth.... also I was reading Test results made in 1942 (No jokes plz) about actual deaths at rated power and times when i was doing my PAT testing Ill see if i can dig them out.
 
An American researcher named Charles Dalziel performed experiments with both human and animal subjects to determine the effects of electric currents on the body. A table showing his research data is presented here:
01703x01.png

[TABLE="align: center"]
[TR]
[TD="align: center"]
[/TD]
[/TR]
[/TABLE]

Important Note: Dalziel's human test subjects were men and women in good health, with no known heart conditions or any other abnormalities that would have compromised their safety. In other words, these data points represent best-case scenarios, and do not necessarily reflect the risk to persons in poorer states of health.
Assuming a skin contact resistance of 600 Ω for a sweaty hand, 1000 Ω of resistance for foot-to-ground contact, 50 Ω internal body resistance, 70 Ω of resistance through the soil from the person's location to the earth ground point, and a male victim, calculate the amount of voltage necessary to achieve each of the listed shock conditions (threshold of perception, pain, etc.) for the following circuit:
01703x02.png


shame could only find American ish version
 
I like this thread also its a funny thing as i watched a program, where a Test Dummy was in a bath and he died every time above 6mA or was it 6ms, LoL it was one of them, Age I suppose still maybe one member here could find out truth.... also I was reading Test results made in 1942 (No jokes plz) about actual deaths at rated power and times when i was doing my PAT testing Ill see if i can dig them out.

Are we still talking deceased souls moose lol
 
Hi All,

I recently heard about the sad death of Emma Shaw who was electrocuted mopping up a water leak in her airing cupboard, apparently a plasterboard screw had caught a cable and caused the metal stud partitioning to become hazardous live!
Strangely the problem was then blamed on a lack of insulation resistance testing even though an insulation resistance test will only measure the resistance of insulation between circuit conductors; and circuit conductors and earthed conductors???
The partitioning upstand could not have been earthed or the over-current protection device would have automatically disconnected the circuit the first time it was switched on!

Any thoughts?
David, I'm not actually aware that the construction used metal stud partioning, or that any became live.
No the problem was not blamed on lack of IR testing, it was blamed on incompetent testing by an inexperienced person conducting the I&T, and by poor supervision on behalf of the QS.
Additional blame was ascribed to drawings not indicating the position of prescribed zones.

The design had been conducted in accordance with the 16th edition, and if had been conducted in accordance with the 17th edition, the particular cable most likely would have been provided with 30mA RCD protection.

As far as I'm aware, 6mA is all that is required to cause an adult male healthy human heart to cease functioning.
Depending upon age, health, etc. individual cases could require more or less current to cause the heart to cease functioning.
A current of 30mA through the body from one hand to the other, may or may not cause 6mA to flow through the heart.
As with any conductor, skin effect would in many instance cause any current to travel on the outside of the body, rather than through the inside.
A bodie's conductivity varies depending again upon age, health, etc. but also upon air density and humidity, how recently a person has been immersed in water, on many various factors.
 
Last edited by a moderator:
h.mmm
Inadequatetesting leads tounlawful killingverdict​
In December 2007, EmmaShaw, a 22-year old mother,was electrocuted in the airingcupboard of her flat in theWest Midlands.At an inquest into Miss Shaw’sdeath, the jury heard how thetragedy resulted from aplasterboard fixing screw beingdriven into a concealed cablewhen the flat was being builtthe previous year, causing themetallic frame of the partitionto become ‘live’ when theelectrical installation wasenergised.The damage to the cable hadnot been detected becauseinsulation resistance tests hadnot been carried out properlyon the wiring, the jury was told.The fault had remainedundetected until water from aleak in a hot water cylindercame into contact with themetal partition. This causedwater on the airing cupboardfloor also to become ‘live’,which led to the electrocutionwhen Miss Shaw attempted toturn off the water stop cockwhen in contact with the water.As the flat was on the firstfloor, no RCD protection hadbeen provided.Her son, then aged 23months, had been shut in theliving room while his motherwent to tend to the leak.Last December, after listeningto two weeks of evidence, theinquest jury found that theinitial testing of the electricalinstallation in the flat by theinstalling contractor, AnchorElectrical and BuildingServices Ltd of Staffordshire,was “not carried out to aprofessional standard, if at all”.Evidence at the inquestrevealed that when theelectrics were installed, aseries of errors were made.These included an unqualifiedelectrician’s mate testing andapproving the wiring in the flat.The inquest heard that foursafety documents that themate had filled out, and whichwere checked by thecompany’s supervisor, also hada number of errors in them.The jury said that there hadbeen a “failure by thecompany to assess thecapabilities of their workforceand constantly monitor theirdevelopment” and a “failure tocomply with their health andsafety standards”. Theyconcluded that Miss Shaw hadbeen unlawfully killed.Following the verdict ofunlawful killing, the Health andSafety Executive confirmedthat new evidence would bepassed to the CrownProsecution Service, whichhad previously said that therewas insufficient evidence tosuccessfully prosecute anyone.The Coroner told the inquestthat he would use coroner’srules to write to the NICEICand other relevant bodies,asking if anything can be doneto curb the practice ofelectricians signing safetycertificates based solely oninformation reported to themby others.​
Thanks to the E SwitchedOnIssue 24 Spring 2012, p13 forthis update.​
The coroner at the inquest into the death of22-year-old mother Emma Shaw asks whether​
anything can be done to avoid similar tragedies
 
Tragic. However, one point. If a screw has been driven only into the live wire, you could IR test it all day long until your battery ran out and get perfect results every time. If the screw had gone across L to N or E then the fuse would have blown.
 
h.mmm
Inadequatetesting leads tounlawful killingverdict​
In December 2007, EmmaShaw, a 22-year old mother,was electrocuted in the airingcupboard of her flat in theWest Midlands.At an inquest into Miss Shaw’sdeath, the jury heard how thetragedy resulted from aplasterboard fixing screw beingdriven into a concealed cablewhen the flat was being builtthe previous year, causing themetallic frame of the partitionto become ‘live’ when theelectrical installation wasenergised.The damage to the cable hadnot been detected becauseinsulation resistance tests hadnot been carried out properlyon the wiring, the jury was told.The fault had remainedundetected until water from aleak in a hot water cylindercame into contact with themetal partition. This causedwater on the airing cupboardfloor also to become ‘live’,which led to the electrocutionwhen Miss Shaw attempted toturn off the water stop cockwhen in contact with the water.As the flat was on the firstfloor, no RCD protection hadbeen provided.Her son, then aged 23months, had been shut in theliving room while his motherwent to tend to the leak.Last December, after listeningto two weeks of evidence, theinquest jury found that theinitial testing of the electricalinstallation in the flat by theinstalling contractor, AnchorElectrical and BuildingServices Ltd of Staffordshire,was “not carried out to aprofessional standard, if at all”.Evidence at the inquestrevealed that when theelectrics were installed, aseries of errors were made.These included an unqualifiedelectrician’s mate testing andapproving the wiring in the flat.The inquest heard that foursafety documents that themate had filled out, and whichwere checked by thecompany’s supervisor, also hada number of errors in them.The jury said that there hadbeen a “failure by thecompany to assess thecapabilities of their workforceand constantly monitor theirdevelopment” and a “failure tocomply with their health andsafety standards”. Theyconcluded that Miss Shaw hadbeen unlawfully killed.Following the verdict ofunlawful killing, the Health andSafety Executive confirmedthat new evidence would bepassed to the CrownProsecution Service, whichhad previously said that therewas insufficient evidence tosuccessfully prosecute anyone.The Coroner told the inquestthat he would use coroner’srules to write to the NICEICand other relevant bodies,asking if anything can be doneto curb the practice ofelectricians signing safetycertificates based solely oninformation reported to themby others.​
Thanks to the E SwitchedOnIssue 24 Spring 2012, p13 forthis update.​
The coroner at the inquest into the death of22-year-old mother Emma Shaw asks whether​
anything can be done to avoid similar tragedies

16th Ed - not 17th, so unlikely RCD protection would have been a factor at all. Possibly earthing wouldn't have been a factor either - though one has to question where the bond to the water main was.

Additionally, insulation testing would not have revealed any fault had the screw pierced only the outer sheath and the live insulation.
 
These are the reports in the papers at the time:
Young mother electrocuted as she mopped up water from leaky boiler died after catalogue of workmen's errors | Mail Online
Mother electrocuted after mopping up in kitchen, inquest rules - Telegraph
Electrocuted West Bromwich mum Emma Shaw was killed unlawfully, inquest jury rules - Birmingham Mail
It appears that the inquest jury were more concerned that other tradesmen were not made aware of prescribed zones, and the lack of drawings detailling the zones than with anything else.
As far as I'm aware, prescribed zones have been in use since 1966, the 14th edition.
The Coroner appears to be more concerned about the NICEIC practice of allowing one Qualified Person to act as a QS for a number of unqualified persons.
It appears from some of the articles, that some of the testing was not actually conducted by an employee of the company, but by a friend of an employee.
I would expect IR testing to show such a fault, if metallic studwork had in fact been used.
 
It's hard to read between the lines, metal studwork, as said above would result in fuses/breakers operating, im wood work would just sit there until someone or something conductive touched it.
 