Hi All,
If you match the I2 value of BS EN circuit breakers to the current carrying capacity of T&E cable a 4.0mm final circuit (referred to generally as a radial) should be protected by a 20amp circuit breaker.
The same theory also means that a 2.5mm T&E ring final circuit should actually protected by a 25amp BS EN circuit breaker!
2.5mm final circuits (referred to as radial) should be protected by 16amp BS EN breakers.
1.5mm - 10amp BS EN circuit breakers.
1.0mm - 6amp BS EN circuit breakers.

Now it makes perfect sense to adopt this thinking for two reasons:
First it is more efficient therefore saving the planet and will prevent overloading of cabling therefore reducing the risk of fires.
Second it will provide work for unemployed electricians.
 
Now it makes perfect sense to adopt this thinking for two reasons:
First it is more efficient therefore saving the planet and will prevent overloading of cabling therefore reducing the risk of fires.
Second it will provide work for unemployed electricians.

Insane!!!
 
hope a mod comes on soon and closes this pointless thread.
another day, another crap post!
 
The current carrying capacity of your cable should be greater than the I2 value of your circuit breaker (unless you are supplying a machine with heavy starting current) so why the hostility?
 