If you match the I2 value of BS EN circuit breakers to the current carrying capacity of T&E cable a 4.0mm final circuit (referred to generally as a radial) should be protected by a 20amp circuit breaker.
The same theory also means that a 2.5mm T&E ring final circuit should actually protected by a 25amp BS EN circuit breaker!
2.5mm final circuits (referred to as radial) should be protected by 16amp BS EN breakers.
1.5mm - 10amp BS EN circuit breakers.
1.0mm - 6amp BS EN circuit breakers.
Now it makes perfect sense to adopt this thinking for two reasons:
First it is more efficient therefore saving the planet and will prevent overloading of cabling therefore reducing the risk of fires.
Second it will provide work for unemployed electricians.