The regs air on the safe side of the current capacity of cables anyway.
Exactly Rob. I've seen 25mm tails take 250 Amps before the sheath starts melting, never mind the cable.
Hope the op posts up a link to where I can buy his book/s? Thing is I dont know if poundland have an online shop pmsl :rofl:
david911cockbur, I hate to tell you this but…..
[video=youtube;oAKG-kbKeIo]http://www.youtube.com/watch?v=oAKG-kbKeIo&feature=youtu.be[/video]
Darkwood - basically we are allowed to multiply the I2 value by a fusing factor when designing circuits for machines with a heavy starting current.
The basic principle of over current protection is to avoid small overloads of a long duration - now if you understand that but still believe that you can effectively protect a 36amp cable by using a circuit breaker that will not operate below 46amps, then you have obviously lost any grip that you may once have had on reality!
Just gonna go get me some of this
IMO a 4mm2 T&E cable will carry 37amps when clipped direct.......................A BS EN 60898 B,C &D circuit breaker >63amps has an I1 (non-fusing factor) of 1.13In and an I2 (fusing factor) of 1.45In.....therefore a 32amp CB will trip on over load between 36 and 46amps and above.......although upto 46amps it may take longer than the conventional time of 1 hour, but it will trip........so I suppose you could have small overloads, but IMO not for long enough durations to damage the cable......
Your stubborness is beyond belief ..... have you not realised that you are so isolated in your opinion on this that its time to say you may be wrong, consider a T&E rated at 36amp now it will happily do loads up to this indefinately but as you creep past its rating and passed the little buffer zone applied for safety then you start getting heat generated with a small % over the ccc of the cable, the copper isn't going to melt nor the insulation break down it will maintain integrity even if the mcb takes 10's of hours to trip (although a circuit which allows this is incorrectly designed and should be avoided) As the current rises further still above the ccc of the cable then running temp' rises and standard T&E is 70c before it would start to break down but heres the science bit .... the higher the current is above the ccc the higher the temp may get but with the time curve chart for the protective device taken into account the higher temp will be for a short enough period to stop the cable been damaged.... consider a short circuit and the current flow!!!! instant trip protects cable.
These calculations are not just picked out of thin air ....overload situations have been factured into the calculations you use and the tabulated ccc of cables.....
I design - install - and fix machine control systems that in some cases is crucial i know the tolerences and breakdown points of cables i use, cable temp' rating i come across need to withstand 100's of degrees and if i calculate incorrectly a machine could be on shutdown at great cost so i would appreciate it if you dont lecture me about basic house bashing mcb ratings with regards to cable ccc.......
I suggest you contact the institution of Engineering and Technology who are a key input into the regulations and the calculations we are taught and tell them they have got it wrong.... but hope you have all the relevant thermal dissipation research of both the pvc insulation and the pvc environmental protective outer sheath of your T&E just as a starter..... why do you think we have to down rate the ccc of a cable when grouped or through thermal insulation; because it cant dissapate its calculated generated heat as fast!Small
Small overloads of short duration are acceptable and can be frequent in ring circuits but the cable isn't going to explode.
May i just edit here to save me from apparent reg contradiction with regards to this post.... 433.1- Every circuit shall be designed so that a small overload of long duration is unlikely to occur so with all due respect the situe should not happen if you design you circuit correctly anyway.
Your stubborness is beyond belief ..... have you not realised that you are so isolated in your opinion on this that its time to say you may be wrong, consider a T&E rated at 36amp now it will happily do loads up to this indefinately but as you creep past its rating and passed the little buffer zone applied for safety then you start getting heat generated with a small % over the ccc of the cable, the copper isn't going to melt nor the insulation break down it will maintain integrity even if the mcb takes 10's of hours to trip -any longer to trip and the overload is probably too insignificant to be worth consideration as a safety issue. As the current rises further still above the ccc of the cable then running temp' rises and standard T&E is 70c before it would start to break down but heres the science bit .... the higher the current is above the ccc of the cable the shorter will be the time scale that it is overloaded as you will see on your current time curves.
I suggest you contact the institution of Engineering and Technology who are a key input into the regulations and the calculations we are taught and tell them they have got it wrong.... but hope you have all the relevant thermal dissipation research of both the pvc insulation and the pvc environmental protective outer sheath of your T&E just as a starter..... why do you think we have to down rate the ccc of a cable when grouped or through thermal insulation; because it cant dissapate its expected generated heat!
I was patiently waiting for someone to explain the reasoning behind the co-ordination of cable sizing and protective devices. Saved me a good few minutes of typeing!! lol!!