Need a permanent power supply in there really and ill do the work and just get a spark to do the wiring at ends to bypass that payment stuff.
 
Firstlly, there will be a reason that it is £500!!!
Secondly, 6.0mm SWA is not ok to use. There is too much volt drop for a 40amp supply. You will end up with 190v or something at the shed and then your appliances wont work.
Thirdly, if 6.0mm SWA was ok then it doesnt mean to say that 6.0mm twin and earth would be ok as they may have different current carrying capacities due to thermal properties.
Fourthly, and as posted earlier, it is not the number of sockets that you need to know but the loads of what you are plugging into them at the same time. Add this up with your lighting and this will give you a total load.
Fifthly, you have answered my question as to whether you are training or a DIY'er
Sixthly, if you dont want to pay £500 or whatever a professional electrician will charge to di it safely then could i suggest that you get a battery powered stereo and a candle?
 
The quote i had for 500quid was off a professional spark and he said 6mm swa hence why i thought 6mm swa would be ok been told on here that 4mm would be ok this is why im confused even if i get professional in id want to lower my cost by getting bits and pieces in myself
 
type in to Google, cable size calcuator and have a look for yourself. your 40a load is 9.2Kw or 9200w. See what it says.

If that sparks has priced that for 6.0mm cable then he is either not giving you 40amps or he is nuts. Are you sure he is qualified and part p registered?
 
The quote i had for 500quid was off a professional spark and he said 6mm swa hence why i thought 6mm swa would be ok been told on here that 4mm would be ok this is why im confused even if i get professional in id want to lower my cost by getting bits and pieces in myself

So you come here to get other professionals to tell you how to do it. Oh dear.
 
Have you got any other services entering the shed?
is there Rcd protection? Unless your installation methods don't require one.
 
PME, export or not to export that is the question, or shall we TT or not to TT that is the question. But we are none the wiser as we have not got all the information.

Mean while back at the ranch, i will sit back and wait for the forum posse to throw there trade mark comments into the ring.

FYI younglearner the forums are/were/nearly done;,,,, setting up a trainee area with mentors and alikes, speak to admins they can advise better on the progress of this idea
 
Actually I think the £500 is probably about right and I'm guessing he's not digging a trench for this cost.

Now what about the bonding in the house??
 
£500 doesn't leave much after 80m of swa.

And definitely doesn't leave enough to get a mini digger in.
 