Hi, could any one help me out with this one. I've got to do do a ze test on a pme system. What is the maximum result allowed and is it still a 3 wire test as the neutral is the earth. What sort of result should I be looking for. This is only because my uncle has just been put on a pme system and he asked me to make sure it's ok, not for anything official. Thanks
If he has just been provided with a PME then don't worry, it will have been tested when installed and will conform to the allowed limits.
Absolute TOSH.
Consult your OSG for the maximum you are alllowed and then check with your MFT.
hes really paranoid about anything like this and has given the electric company loads of grief and they wont take any responsibilty as in telling him its tested and ok. they want an electrician to test it independantly and then he has to phone them back and confirm before they will close his case down. he was on a tt an had a hard time getting them to change him over. if any body can tell me the maximum result allowed so i can make sure its under i would really appreciate it.
0.35Ω. 2 wire test, L-E. use the hi-current setting on your MFT.
just spotted that he's asked and had the question answered before. i'll let him sweat over the next one.
sorry, started a new thread as im new to the site and was having trouble finding the thread i started before (found it now and all sorted). i cant find my osg and i have a good mft. im going there now so was trying to sort this now. telectrix answered my question and im good to go. thanks again to him
- - - Updated - - -
There's onl one place to keep your OSG, and thats in your tool kit, which should adjacent to your MFT.
just download the app. or watch how to do on you boob