benji
are we seeing enough of the drawing to find the problem?
You are on the right track...you just need to look a little closer at the details posted....(K1)Im puzzled a bit as you say it was reported as an electric heater overheat which would suggest airflow loss, now this system should have air flow senses to shut heater off long before it overheats but thats another issue as i said i cant see the way the system works and thus not sure what and when which motors and heaters should be active and when not... its easy to see a fault if your familiar with how the system works in the first place. I feel the way you have presented the thread means we are probably overlooking the obvious but can you tell us how the system would normally work and what fans should be on or off when heater bank is needed?
All i see is if K1 or K2 are not closed then the orange relay cant pull in but again you supplied partial info and want us to pick the relevant parts of it.
Did you look closely at the wiring diagram for the K1 contactor?Well only other thing K1 as you have stated is intake fan full speed and all i see on the output is the loop to K2 and 2 wires one of which goes to signal the speed controlled fan so i can hazard a guess its lost control of the intake fan and is now pulling in a speed controlled unit which if set at low speed which will allow for overheating on heater bank if set to run slow.
ok but got to ask where are the overloads
Yes that's correctso the thermal protection are the 2 symbols shown on each motor wired in series
Yes, you were on the right track. If you look closely, you can see the U1 marking on the brown wire but it is not connected to the contactor K1, as per the wiring diagram.I did point out i couldn't see the wiring to the motor, i can see the loop to K2 contactor as per drawing and the brn tap off for the relay, the grey wire double up on the 2nd output of K1 i said i wasn't sure what that was for .... the picture wasn't clear enough to work out you issue as we cant follow wiring by sight and the cables are not number coded correctly....... i would be supprised if anyone could pull that from the info supplied but given the up hill struggle i guess i was as close as i could be given the info supplied......
Im aware that there are thermal cutouts in the motors but i still believe this system would benefit greatly from contactor overloads with thermal and magnetic trips, in any control system i only wire the thermal trips as a redundency in case of failure of other overload monitors, judging by the very basic lack of organisation, clear design flaws etc i can't believe it can comply to the appropriate BS standards...... although we are missing part of the diagram the thermal trips will probably reset automatically, is there any thermal monitor relays to hold supply out instead of allowing a reset button to be pressed on the operator controls thus putting the motor under repeated stress which can reduce its life if not destroy the windings.