It is a nightmare reading those calculations, try and spread them out a bit.
If you are using the adiabatic equation you need to know the characteristics of the breaker you are using.
If you are using a BSEN60898 10A type C MCB and look at the graph for those breakers a fault current over 100A is off the chart, so you could say (though this would give a high csa) 100A fault current will cause a trip in 0.1s and use these values in the adiabatic equation.
Uo/Zs being used to calculate the PFC would be 230/0.378 and you would multiply by the rule of thumb value of 2 to get a prospective fault current of 1216 Amps. Therefore the breaker would trip far faster than 0.1 seconds, but unless you haev the I2t values for the breaker from the manufacturer you cannnot tell how fast or how the current limiting effect operates.
So using the 100A value of 0.1s trip time would give you a minimum cpc size of 0.28 mm2.
Minimum cpc allowable is 1 mm2.