if the golf club has a 3 phase supply then a submains to the grounds keepers hut is feasable.
applying diversity realistically its unlikely to draw more than 40A continuous.
still though biff....thats virtually a 2 bed house....
what are they doing...living in this shed or what?
i mean 12 points, 6KW cooker...chuffin showers...
next it`l be ikea beds going in....
 
'Shed' my chocolate star-fish, sounds more like a dozen Polish/Latvians/Romanians will be moving in on the QT.
 
Then it would be over specced.
The most they would get would be 1 twin socket and 1 light.

I'd be thinking the groundsmen might be growing something.
`overspecced` isn`t the word...
this is a load of bolloks is this one....
 
You're all being beastly.... I think that the least any good groundsman deserves is fully heated accomodation, range style electric cooker, nice hot shower plus enough sockets to power exercise machines, hifi equipment, widescreen TV's, a coffee machine, and leather reclining layzeeboy chairs...
 
[a dozen Polish/Latvians/Romanians will be moving in] that may be closer to the truth than realised...lol...
I come from Guernsey, where this is quite normal. Mostly greenhouse packing sheds. Some time ago there was a fire at a greenhouse site and loads of people were seen in their pajamas fleeing clutching duvets.
 
I come from Guernsey, where this is quite normal. Mostly greenhouse packing sheds. Some time ago there was a fire at a greenhouse site and loads of people were seen in their pajamas fleeing clutching duvets.
aye and its despicable...
my concerns are what happens when the floodgates open again to Mr. bulgaria et al?
because we`v got to meet `EU quota`s`
they will all be `sparkys` or `plumbers` or summat you mark my words.....
its gonna be hell....
 
aye and its despicable...
my concerns are what happens when the floodgates open again to Mr. bulgaria et al?
because we`v got to meet `EU quota`s`
they will all be `sparkys` or `plumbers` or summat you mark my words.....
its gonna be hell....

Even if they aren't, it'll only take them 17 day's or so, to become registered with a welcoming scheme provider!! lol!!
 
Had meeting today and 6Kw cooker scrapped now! aparantly they can live with a microwave, hard life eh.
Still shower, but then just a few sockets, lights and a 3Kw water heater. The existing supply we are coming off is a single phase supply, but with nothing on it just the meter there so with a big enough cable (prob 25mm) should be ok.
Thanks all for your input :)
 
from your posts it seems like you are simply guessing the cable your are going to require ??


do some cable calcs or this could end up being a very costly job ! :hammer:
 
from your posts it seems like you are simply guessing the cable your are going to require ??


do some cable calcs or this could end up being a very costly job ! :hammer:

agreed.
you need an Ib first , youre not going any further without a design current.
then you can choose a cable that will give you less than 6.9v volt drop over the 100mtrs ,
which you will to need to achieve to get the lighting operating properly
 
agreed.
you need an Ib first , youre not going any further without a design current.
then you can choose a cable that will give you less than 6.9v volt drop over the 100mtrs ,
which you will to need to achieve to get the lighting operating properly


true words biff

quite a decent length of run there too ! VD would be an issue
 