timhoward

~
Broke Internet
Esteemed
Arms
A BG fused connection unit, with neon.
A boiler.
Fuse out. Spur switched off.

I was checking polarity after a colleague had 2nd fixed it and without thinking chose the load N not the supply N.
This led to discovering:
120v between Supply Live and Load N
120v between Supply Live and Load Live

I tried his 2 pole tester, same except that one said 50v.

Look at boiler end, all fine.
The strangeness stops when I disconnect earth at the boiler.

IR tests L-E and N-E at boiler (at 50v) were >99M

Should I conclude that there's are very very high resistance L to E and N to E paths inside the boiler and yet the impedance is low enough to light up a tester, or am I missing something embarrassingly basic?!
Thanks
 
1703026504215.png
1703026525246.png
 
Another possible explanation is that if the boiler has any sort of traditional interference filter in the mains input, this will lead to the 120V effect, as there is a capacitative divider across the mains, with the centre point earthed. This has cropped up on previous posts here with other appliances. It depends a bit on the impedance of the measuring device as to what voltage you see, but with high impedance you will get half mains voltage across each CY capacitor.
IMG_0413.jpeg
 
Thanks, both of you!
The filter concept was vaguely in my mind but I’ve never been told the reason or seen a diagram before.
 