Folks need advice. House I am working on. TT earthing. The rod is closer to the gas pipe/meter box than the Consumer Unit. I wondered why I could find no bonding conductor in the CU. It appears someone took the Main Earth 16mm cable from the earth rod to the gas pipe and then onto the Consumer Unit. The cable is not broken and continuous. II can't see this being correct but can't establish where in Regs it's not compliant. Maybe I am too fussy as I like to see bonding conductor's on the MET not going hunting for them. Am I right, if so where in Regs?
If so I am impressed. Yes it did not feel right to be honest and often my gut reaction has been right.. Maybe I should rely on that a bit more. Obviously this has been done by the gas Installler a few years ago. I had looked through section 5 of the Regs but sometimes I find interpretation is everything. Totally agree with your assessment and will help greatly. Thankyou