Thousands of consumer units are like this.No code from me.So big hole at rear of CU.. right next to nice dry timber. I feel like a C3 is appropriate, but is there any legitimacy in coding it a C2?
View attachment 125294
Yeah my finger can just barely reach the hole (I have a pic showing my finger tip peeping through), but certainly can't reach any live parts.I would give it a C3. I would only give it a C2 if you could access that hole and actually get a finger inside, from the outside, which I doubt you can.
Thanks for your input Bob. Personally I don't attach too much weight to how many are like this, but appreciate your thoughts. Good to get a few sets of eyes on this. Cheers.Thousands of consumer units are like this.No code from me.
Remember that if you are designating it C3 then you are stating that it fails to comply with at least one Regulation, so perhaps ask yourself which specific Regulation(s) It contravenes.Yeah my finger can just barely reach the hole (I have a pic showing my finger tip peeping through), but certainly can't reach any live parts.
I'll see if anyone else has any contributions but otherwise I'll go with a C3 - cheers.
That's interesting, and a very good point if correct. I was considering giving it a C3 simply because the spark that installed it could've mounted it directly onto the plastered brick wall and used the cable entries along the top surface of the board - the way he's done it is less safe in terms of a fire spreading from the consumer unit (so I suggested improvement), but may not directly contravene a regulation. So you're saying that even though we probably all agree that it would be safer mounted a different way, if it doesn't contravene a reg it can't be coded?Remember that if you are designating it C3 then you are stating that it fails to comply with at least one Regulation, so perhaps ask yourself which specific Regulation(s) It contravenes.