I changed 3 x 125A fuses for 3 x 125A D type MCBs (ABB). They held for a day and then two started tripping, we didn't have any spare 125A, so we fitted 100A C type and the issue has disappeared, can anyone shed any light on this for me please?
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc