mcb

  1. S

    Lighting MCB keeps tripping after changing the kitchen light

    I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from Screwfix). Although the light turned on after flicking on the MCB, when you turn it on or off the MCB trips, and sometimes the RCD, too. I removed the...
  2. S

    32Amp MCB tripping initially and then staying on when pushed back up?

    I have a 32amp MCB for my heating (heat pump) and when the heating comes on, it trips after a few seconds. If I push it back up it works fine until the next time the heat pump calls for power. I thought it might be faulty so I swopped it out but had the same issue with the new one. What might...
  3. finhudson16

    Seemingly under-rater MCB for wire size

    Hi All, I'm looking at installing an induction hob in my kitchen (upgrade from gas) and I gather that it can be added to the cooker circuit if there's enough capacity. In the fuse box and at the cooker end, the cooker circuit is wired in with 6sqmm cable, but only has a 16A MCB which I gather...
  4. timhoward

    MCB trip (not RCD) during loop test

    I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and with some misgivings I agreed to use it. It came to testing. Zs@DB of 0.3 ohms in garden room. CPN RCD main switch tripped x1 at 21ms The lighting...
  5. M

    C type MCB time and Log logs

    Hi guys Have a circuit its OCPD is a C type 80A 10ka 60898 MCB with a pfc of 1.11ka. On the log log graph for this device I’m struggling to understand the time for it. It only goes to 800a? I’ve spoken to the NICEIC who say it would operate withing 0.1 seconds but I’m struggling to see how...
  6. timhoward

    Lewden MCB compatibility

    Hi all I can't remember if the current range of Lewden MCBs fit these boards? It's to supply SWA so RCBO not needed. Thanks for any help.
  7. A

    A MCB 1200+ amps tripped .. help is needed urgent

    Hi I'm supervising maintaining a building powered by a 1250 Amps and i had a total blackout twice within a week. Checking the MCB and it's healthy and checking the REF is also fine and it has been reset normally. What would make such MCB trip? Sorry but no photos are allowed to post by the...
  8. Other_Tucker

    How do I enter reports when two circuits are in one MCB

    For example the house today had two lighting T&E in the same MCB. I know it's fine, but as I test both 'radials' where and how do we enter them on an EIC/EICR form on the NICEIC online certification thing? I can make extra lines on the circuit chart, but do we write them down as MCB-8a MCB-8b...
  9. D

    Correct MCB sizing or not

    Hi, I recently discovered at my brother in laws that he has a circuit which feeds a outbuilding, but we also discovered that it’s attached to a small part of the downstairs sockets towards the rear of the house! The concern is this outbuilding then goes on to feed another small shed.. is this...
  10. J

    Wiring an MCB beetwen RCD and Main switch

    Good evening, I wondered how the MCB between RCD and the Main switch is wired while watching this video. Photo attached. I assume a busbar link is connected to the main switch and mcb. Do the line conductors and the busbar connected at the same terminal and then go to the RCDSs? Link to the...
  11. rajemessage

    A 2000-watt dishwasher is running on 6 amperes, C grad MCB, how is it possible?

    I have by mistake used 6amps C grad MCB on a 2000-watt dishwasher. though I was asked to put 10 amps. but it is running properly. how it is possible and is it safe? thanking you.
  12. V

    Rats and tripping MCB

    Can i just check something. If a rat decides to chew a cable will it trip the MCB or RCD ? I ask because I had one house recently that had a randomly tripping MCB and it turned out to be a chewed cable. I was surprised as i would have thought it would trip the RCD but it never did. A chewed...
  13. O

    Does SPD MCB size matter?

    Does this matter? I've fitted a Fusebox consumer unit and I didn't have enough 32A MCB's but too many 6A's. The SPD is fed from a 32A one, what's the deal with swapping them around. They are voltage operated not current operated so should be fine right?
  14. R

    If a type B MCB doesn't trip unless 5x nominal rating is hit, what's to stop the cable burning up?

    Just reading through my Student's Guide and wondering about nominal amperage. If guaranteed trip is 5x nominal amperage, what's to stop 2.5mm cable on a 20a radial circuit from running at 70a or something and completely destroying the cable/potentially your house?
  15. M

    Adding a light to a mcb

    Hello I have moved into a new house and the electric meter and consumer unit are under the stairs. What i want to do is put a door there so can use for storage. The problem i have there is no lighting there. So i want to install a ceiling pendant, the easiest way i can see doing it is running...
  16. S

    Why MCB and Fuse cant protect Voltage Surge?

    Hi Everyone, I got some Power Module damaged cause by Voltage Surge. My device protected by 25A MCB and Fuse. Why my device still damage although its already have the protection? Any other way to prevent this from happening again?
  17. R

    Lighting circuit trips RCD but not MCB, can’t find E-N fault

    Long shot but thought I’d try, have a lighting circuit that trips the RCD as soon as the neutral touches the neutral bar for said RCD. Bypass that and it works fine just on an MCB so would think earth-neutral fault, but doing an IR test between N and E shows as a pass (>99M ohm). So unsure of...
  18. Dvyj123

    Hottub mcb selection

    The hottub is 8.1kw so will be 35A max output , I’m going to put it on 6mm 3core swa to an isolator then to the hottub. Would a 40a b type be sufficient for this ? Or would it be better to put it on a 40a c type mcb? Thanks
  19. D

    How to calculate an MCB size

    I am doing a campervan conversion and have a 16A/250V shore power connection coming into a consumer unit which has two breakers - one for the AC input into a Victron Multiplus inverter and the other to go to a plug socket for non inverter loads. I would like to know how to size the MCB for the...
  20. M

    UK RCD rating in Sub board less than suppy protection

    I have a 40amp RCD downstream of a 50a MCB (10mm csa cable) should the MCB be lowered to protect the RCD from overload? If so why does this not apply to RCD devices in Split Load boards