See 250.32(A)You will need to find the article in the NEC which you should know is article 250 of the NEC
See 250.32(A)You will need to find the article in the NEC which you should know is article 250 of the NEC
Your close but read the exception to that particular article. That’s why I say pull 4 wires with one of them being the grounding conductor from the main panel. Think about it you don’t need ground rods at the building because you already have it through your equipment ground.See 250.32(A)
I can tell that you haven’t dealt with any inspectors. I’ve wired many buildings and garages and I have never drove a ground rod at any of them and I haven’t felled inspection. Let’s move on and quit arguing and we will agree to disagreeThe exception is for a single branch circuit, including a multiwire branch circuit, a feeder still requires a electrode. The exception makes sense when you want to have a 20A circuit to a shed for a light, and/or receptacle(s), for example. Unless somebody was under a very old NEC, a 4-wire feeder is required, code permission for 3-wire feeders is long gone & a grounding electrode is still required for a separate structure unless a single branch circuit.