Hi guys - seeking an opinion or possibly experience of the same issue.
I have a spark engaged to do a fair bit of upgrade, been here for 35 years so current installation is well behind current regs !
The main job I asked the spark to do was fit a modern consumer unit in my outbuilding / garage. Rightly - he has gone back to the main board and advised the current armoured is only capable of 40 amps under current regs. However it did pass an insulation test. We plan to upgrade to 16mm for 60 amp capable so can later do an EV charge point . I've bought the ducting.
But - as my main house meter is old - he suggested asking for a smart meter - and at same time get an isolation switch fitted. Makes his works easier. Good idea and I arranged this with my Energy provider. It was fitted on Wednesday.
Not happy - he fitted an ordinary modern Economy 7 meter - not a smart one as promised.
Gobsmacked - he said FYI despite the main fuse saying 100 amps there is only a 60 amp fitted. He scratched up the 100amp label. He said refer to your power distributor.
So - question - has anyone come across a main fuse that says one thing and is fitted with another (less) ?
Where do I stand - it's never been touched since original installation.
Now I think I'm buggered. Can't run all that with 60 amp main fuse ?
My electrician says we are stuck and I have to contact SSE.
Does the power distributor have any responsibility ?
Many thanks
 
Many thanks to both previous replies.
My spark assumed we had 100amps 'available'.
So are you suggesting that in a situation like this, my spark would break the seal to check what's really provided ?
I am not a spark but worked in Engineering for years. It seems very sloppy labelling by SSE and is misleading ?
 
Many thanks to both previous replies.
My spark assumed we had 100amps 'available'.
So are you suggesting that in a situation like this, my spark would break the seal to check what's really provided ?
I am not a spark but worked in Engineering for years. It seems very sloppy labelling by SSE and is misleading ?

It's very common. The fuse carrier itself is rated at 100A maximum. The fuse within can be anything up to this value.

I'm surprised your electrician didn't know this.
 
Ok thank you. I am better informed and learnt something
I also now know I can’t complain to SSE but ask for a survey to see what the feasibility is to upgrade the supply (and cost)
I fear it will be tricky as my supply is run through the middle of next door !
 
I'm not an expert in EV chargers, but I'm given to understand that if you have a looped supply, and a 60 amp supply, then unfortunately both of these are hurdles that will need overcoming.
I've heard of instances where DNO (SSE) will unloop without charging. Others know more about this area of electrickery than me.
 
it is common knowledge now that the DNO are leaving 60amps in now
having to try balancing the loads better from the sub stations ,knowing the fact if everbody was on 100 amp the cable might snap crackle and pop.
 
Thanks again for replies.
I've just looked up looped supply and now understand the concept.
Do SSE have accurate records of whether I am on a looped supply, and the supply cable size(s) ? 35 years ago !!
We are very rural, in one of a pair of cottages fed from overhead. The overhead runs about 400 yards to a more substantial set of overheads. I remember 35 years ago the linesman who installed our supply saying there is a 400 amp switch box there for isolating our overhead.
I think this might be expensive - or I just abandon it all and forget the EV charging 'future proofing'. Keep to petrol !!
I'll contact them tomorrow - maybe they will do a survey.
I'd have preferred my electrician to do this but he's ill at the mo.
Thanks all for your support and replies. Though I'm not an electrician I can understand all your replies and what the fundemental issues are.
 
OK just to close this - and I did ask before - how do you guys as sparks find out what fuse is actually fitted ? Do you check the main fuse (ie break the seal) or does the DNO have an accurate record that you can enquire.
Yes - I'm 'disappointed' my electrician didn't check this further - though he did comment that the incoming supply looked a bit small for 100 amps
 
That’s the funny thing;
Our test certificates asks us to fill in a box what size the main fuse is…. But we are not allowed to pull it to find out

we have to go by the sticker on the fuse carrier… which in experience … is either “100A” or “60/80” which still doesn’t help… which is it? 60 or 80?
The carrier is moulded with 100A printed into the plastic, as others have said, that’s the rating of the carrier- the biggest fuse that can go in.

I’m surprised they didn’t fit a smart meter. I thought all suppliers were pushing for them.
I take it that’s because of rural setting and maybe bad mobile signal for the smart communications.
 
Thanks again for replies.
I've just looked up looped supply and now understand the concept.
Do SSE have accurate records of whether I am on a looped supply, and the supply cable size(s) ? 35 years ago !!
We are very rural, in one of a pair of cottages fed from overhead. The overhead runs about 400 yards to a more substantial set of overheads. I remember 35 years ago the linesman who installed our supply saying there is a 400 amp switch box there for isolating our overhead.
I think this might be expensive - or I just abandon it all and forget the EV charging 'future proofing'. Keep to petrol !!
I'll contact them tomorrow - maybe they will do a survey.
I'd have preferred my electrician to do this but he's ill at the mo.
Thanks all for your support and replies. Though I'm not an electrician I can understand all your replies and what the fundemental issues are.

Hopefully they may be able to sort it for you. Let us know what they say.
 
Now I think I'm buggered. Can't run all that with 60 amp main fuse ?
The better EV charges have a current transformer for the main supply and will adapt the charging to keep your total below 60A (assuming the house is below 60 of course!)

So if charging and you put on an electric shower it just throttles the car charge for 10 minutes or whatever you are using it for.

Bigger issue is if you plan lots of electric heating or a massive range-style cooker, though I think some of the fancy induction ones also have total demand throttling (or am I imagining that?)
 

Reply to 100 Amps or 60 Amps in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
692
New member and DIY. I have a 60 AMP breaker going to a sub panel for a workshop. Two months ago I bought an electric car and a 40 AMP charger...
Replies
7
Views
1K
I'm having an extension built and the builder leading the project has said that the electrician will be over in about 4-6 weeks to start his works...
Replies
4
Views
2K
The seller is saying they will not upgrade the electric and it is normal to have 100 amps. However the inspector is stating it may trip often and...
Replies
4
Views
801
Hi I have a customer who has a kiosk with 100 amp cut out fuse supplied from UK power, he needs to bring the power 178 meters to his house, He...
Replies
8
Views
897

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock