Cheers lads I’m going to email the consultants that issued the drawing in morning to ask what they specifically require I’ll let you know what they come back with
 
Will be interesting to see what they have in mind. It is possible the 32A primary MCB was chosen to deal with switch on surges, but it may be better to use something like a 16A or 20A D-curve MCB instead.

Protecting the output wires to the sockets in the (hopefully unlikely) case of a short still seems to be missing but hopefully you will hear by tomorrow or Monday.
 
He's already got double pole MCB's in the socket, why does he need additional double pole MCB's in a DB? I suppose it all accords how long and vulnerable the lead are.

For the same reason we supply socket circuits from an MCB when every plug has a fuse in it.
The circuit feeding the socket needs to be correctly protected for overcurrent and fault.
 
I guess it also falls under 433.2.2 as the cables are longer than 3m and the output of the transformer could reasonably be taken as a "point where a change occurs".
 
Why don't building site transformers have MCB's on the fly leads to what they are supplying?
Some do it seems, from the Blakley data sheet:

Overcurrent Protection
Input MCBs are Type “D” and output MCBs are Type “C”, to BS EN 60898.
All 32A sockets are individually protected by 32A DP MCBs.
Lighting circuits without RCD are protected by 10A or 16A DP MCB, as detailed above.


Taken from this product:
Their 4kVA one has a 16A DP input breaker, more in keeping with that sort of rating (unlike the 32A mentioned earlier in this thread).
 
Why don't building site transformers have MCB's on the fly leads to what they are supplying?
You have a thermal trip built into the transformer and over current protection and in the 13amp plug top.
larger kva transformer distribution feeding multiple equipment will have over current protection and mcbs on show on the side of the transformer
[automerge]1585905737[/automerge]
Like this type DA538F9E-1EE6-46C0-AF74-65E9668801A9.png
 
Last edited by a moderator:
1.5kva only, not running anything fancy, only a vacuum and a biscuit jointer.
[automerge]1585906153[/automerge]
These are very basic questions for someone claiming to be an electrician

It's been eleven years since I retired and anywhere near a building site so have had to make room in my brain for other things.
 
1.5kva only, not running anything fancy, only a vacuum and a biscuit jointer.
[automerge]1585906153[/automerge]


It's been eleven years since I retired and anywhere near a building site so have had to make room in my brain for other things.

The basic principle of protecting circuits should still be there though surely?
 
It is showing a 10 way dist board with 16A type C protective devices. It doesn't indicate whether single or double-pole devices but it should be double-pole.
 