It is showing a 10 way dist board with 16A type C protective devices. It doesn't indicate whether single or double-pole devices but it should be double-pole.

Oddly it is not showing MCB specified at the sockets, unless that is specified off-page or in the list of parts?

Certainly the ideal solution to me would be a board right next to the transformer (less than 3m cable) and all DP MCB there.
 
Oddly it is not showing MCB specified at the sockets, unless that is specified off-page or in the list of parts?

Certainly the ideal solution to me would be a board right next to the transformer (less than 3m cable) and all DP MCB there.
You don’t need mcbs at the socket positions if you have DP mcbs at the origin of the circuits
 
The spec is poorly worded indicating single-pole and neutral, it should say two-pole and earth.
 