The Building Regulations apply to domestic buildings, Part P makes BSen7671 LAW, it has to be complied with. How well it is enforced is another matter.
Any current work has to comply to the latest regulations, buried cables, special locations etc, etc. You work on a circuit then you take it over, you don't have to re-run buried cables or ones out of zone but you would be expected to add RCD protection as already stated.
My solution is just replace that circuits breaker with a RCBO, £20, job done but still do a continuity and IR test on the completed circuit then a Zs at the bit you modified/added.
Personally I use my own forms to record my circuit test results and put notes on them about the condition of the part I haven't touched just in case some other so&so mods it again after you've left. If your meter is accurate then the readings will be different to those you have on your records if it gets to Court. I also make notes of anything found that is dodgy and put that on the report the client gets so again they can't blame anything on you after as they were too tight (or skint) to pay for needed work. All the report forms have a place on them for 'condition of existing installation', why it's there so the owner can't say they never knew.