Hi all im new to forum so go easy on me.
Just want to ask a question which relates to an armoured sub main now my question is if i wire the armoured to a consumer unit how do u calculate the size of cpc, from the earth bar to armoured banjo. I do know you can use an armoured as the protective conductor, but for example if the cu is plastic then it isnt earthed.
 
Terminate the outer sheath below the CU using an adaptable box and run the cores into the CU. I'd recommend using a 3 core SWA too.
 
Depending on what type of cu it is you may not be able to gland straight to it as many form the removable cover, may be better glanding into an adaptable box next to cu then run some tails or t+e between.
 
To note here for your future ref' regardless whether the consumer unit is plastic or metal you are still required to fit an earth tail from Banjo to earth block...as well as at the load end if the SWA is the earth.
To ease you into the Forum i will keep it simple for now and not list exceptions and overcomplicate things and finally welcome to the forum, good to have another fellow yorkshireman here...
 
Have seen swa into plastic cu as if was metal clad,

- - - Updated - - -

Lug on nut to earth bar
 
Thanks for all the comments guys, if i use a 3 core i could use 1 core as earth, aswell as earthing at both ends from earth bar to banjo or i could be a cheap skate and use 2 core and earth the armourings at each end personally am gonna go for the cheaper option depending the armourings has sufficient csa for fault currents
 