2.5mm 4 core swa clipped direct but 2 core used as line and 2 Neutral swa as earth acceptable?

As long as the SWA calculations is ok for the earth then its ok to parralel up the cores in the 4 core for L & N. Label up the cores correctly though.
[automerge]1569568729[/automerge]
As far as I know this is frowned upon...

Why mate?
 
As Spoon has said, as long as all calcs andtest are ok then perfectly acceptable.
 
As long as the SWA calculations is ok for the earth then its ok to parralel up the cores in the 4 core for L & N. Label up the cores correctly though.
[automerge]1569568729[/automerge]


Why mate?

Frowned upon ? Although it may comply , I always got the feeling among fellow sparks pairing up cores in a multi core cable is a bit naff
 
if it's PME, the SWA armour will not comply as a bonding conductor if such is required.
 
Frowned upon ? Although it may comply , I always got the feeling among fellow sparks pairing up cores in a multi core cable is a bit naff

Its only a parallel circuit in one cable.
 

Reply to 2.5mm doubled up on 4 core in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
714
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
421
Carrying out an EICR and came across a ring final circuit wired to the first of six metal clad sockets in 2.5mm 5 core SWA. Obviously 2 cores for...
Replies
5
Views
924
Hi there , is there anything else to consider when using 5 core SWA instead of 4 core + separate Earth in three phase installations for cable...
Replies
2
Views
854
Ok i may get slated for this one but here goes; A bit of background info first. Its been a while since ive looked at my iee regs, and ive not...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock