the pict

~
Mentor
Following on from a completed job I have been asked to do a install for a staff laundry 4 dryers 4 washers 2 lighting circuits up to me how a carry it out,but they propose bring in 2 phases from the main staff accomodation building so there will be a sub 3 phase board with only 2 live phases, whats the protocol for this I have never thought about this before, using a couple of phases from a 3 phase yes, but bringing in 2 phases for general distribution ???, when I queried it I was told the main reason is they laid the wrong cable 3 core instead of 4, I am not saying I know this is wrong just never heard or seen this done,comments anyone
Pict
 
when I queried it I was told the main reason is they laid the wrong cable 3 core instead of 4
I'd tell them to get knotted and get the correct cable installed. You're talking about a commercial laundry which is a large load so you need to balance it across all three phases. There's also a good possibility some of the equipment may be 3-phase.
 
I also a feeling throwing 4 washers + 4 dryers across 2 phases will cause you big issues the duty i expect will be high as they want so many machines can you give us loads of details cable csa, install method, size of loads existing demand on each phase .... its possible but has alot going against it.
 
Cable is 16mm SWA,I have no idea re what the actuall machines demand is, I had assumed this would have been done before the cable size was decided upon, but yes you have to assume the whole lot could be on at once as this serves 10 members of staff dont know if the machines these are domestic or commercials
Pict,
 
as above posts, i'd advise on replacing the cable so as to bring all 3 phases in. before deciding on what cable to use, you need to know the total load, OCPD ratings and cable csa to handle the load and ensure VD is within limits. it's been done wrong once. don't make the same mistake.
 
Yes I need a lot more info I cant get a hold of the head of projects till Monday but I will be expressing my concerns on this and you are all correct a half ar££ed attempt at a project like this will end in tears and recriminations,
 