is it totally seperate or attached? this is still a greyish area about exporting earths. prob best idea is to tt the extension

It will be totally separate. the outbuilding will be TT, the house PME.

If I do it this way am I right that the SWA should only be earthed at the intake to house and not in the outbuilding?

thanks
harry
 
Hi.

I be looking at a 50A MCB max for the 10mm SWA.

In free air the max CCC for a PVC SWA without applying any correction factors is 60A.

XLPE SWA does have a higher rating but not by much as it's rated to 90 degrees whereas PVC SWA is rated at 70 degrees.
 
Last edited by a moderator:
The customer has now informed me that the workshop is actually going to be a separate building!

The workshop will just have a ring and lights so quite straight forward.

Can I take the supply from the house to the extension containing the shower, lights and ring, and then take another sub main from there to the workshop?

Or, take 2 SWA cables out to the two locations from small CU at intake with separate MCBs and earth both separately?

Thanks
Harry
 
You could do it eiher way, Harry. You don`t mention distance from 1st outbuilding to workshop - if close then may be better to submain workshop from 1st D/B.

If using seperate submains for each then obviously TT each seperately as discussed.
10mm or > earthing conductor, & 6mm or > for MEB when TT`ing

As you thought, earth SWA at supply end only - insulate at individual D/B`s (as per 542.1.8)

If you do feed a sub from the 1st D/B then you really ought to consider upping to 16mm. As Lenny intimated, even XLPE would only give you 58a if buried, so you`d have to drop down to a 50a breaker. That`s too low IMHO to class as a well designed install with all the loading possible. A 16mm XLPE submain would offer more than enough to allow that 63a as you`d first planned.

Hope it`s useful
 