You could do it eiher way, Harry. You don`t mention distance from 1st outbuilding to workshop - if close then may be better to submain workshop from 1st D/B.
If using seperate submains for each then obviously TT each seperately as discussed.
10mm or > earthing conductor, & 6mm or > for MEB when TT`ing
As you thought, earth SWA at supply end only - insulate at individual D/B`s (as per 542.1.8)
If you do feed a sub from the 1st D/B then you really ought to consider upping to 16mm. As Lenny intimated, even XLPE would only give you 58a if buried, so you`d have to drop down to a 50a breaker. That`s too low IMHO to class as a well designed install with all the loading possible. A 16mm XLPE submain would offer more than enough to allow that 63a as you`d first planned.
Hope it`s useful