Hi Everyone ,
I'm always confused that One ohm or less is a must for circuits supplied by a company earth .

But when its an Earth Rod then up to 200 Ohm is acceptable ...
Surely the rod is much inferior so should be less acceptable resistance ..

I know we now have RCD's but Rods were in place long before .

Just curious ..
 
Hi Everyone ,
I'm always confused that One ohm or less is a must for circuits supplied by a company earth .

But when its an Earth Rod then up to 200 Ohm is acceptable ...
Surely the rod is much inferior so should be less acceptable resistance ..

I know we now have RCD's but Rods were in place long before .

Just curious ..
Luka you are right in the US we use 2 ground rods and it’s less than 1 ohm but I think in the UK has sandstone which is very resistant. I understand that UK power companies have different arrangements than we do and I guess that’s your answer and welcome to the forum
 
Before current operated RCDs ,they were effectively
Voltage operated ... but ...
Their big problem was you needed a voltage for them to operate.
Parallel paths to earth could quite easily "supress"
the voltage from ever occurring .
Causing a change of strategy to monitoring the currents in and out , balancing !
( opinions may be available on adequacy /stability ? of 200 ohms -but not from me ! )
 

Reply to 200 Ohm ? in the Electricians Chat - Off Topic Chat area at ElectriciansForums.net

Similar Threads

On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
951
Hi all, Would like some advice on the below. Context: Rural French domestic installation TT system Earth rod is situated inside the property...
Replies
6
Views
968
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock