Currently studying towards achieving my 2391 and revising from GN3 and IEE 2391 exam success

Doing a practice paper and a little confused with the answer to a certain question, can anyone else make sense of it

Question word for word

9. A ring final circuit continuity test is to be carried out on a newly installed circuit, state
Two additional tests that are automatically carried out whilst completing this test

Answer

a) polarity
b) continuity of Cpcs


Now the question has threw me because I'd presume that continuity of Cpcs is obtained in the initial ring continuity test so how is it additional?

And how do I automatically determine that polarity is correct via a ring continuity test? I could still for arguments sake have the Lives connected into neutral terminal in a socket outlet from said ring main in question

Anyone shed a bit more light? I might have missed the obvious here but bear in mind I've been revising for hours
 
Hi all

Currently studying towards achieving my 2391 and revising from GN3 and IEE 2391 exam success

Doing a practice paper and a little confused with the answer to a certain question, can anyone else make sense of it

Question word for word

9. A ring final circuit continuity test is to be carried out on a newly installed circuit, state
Two additional tests that are automatically carried out whilst completing this test

Answer

a) polarity
b) continuity of Cpcs I would have said this would be R1 + R2


Now the question has threw me because I'd presume that continuity of Cpcs is obtained in the initial ring continuity test so how is it additional?

And how do I automatically determine that polarity is correct via a ring continuity test? I could still for arguments sake have the Lives connected into neutral terminal in a socket outlet from said ring main in question.

When you have line and cpc cross connected and you're taking measurements at each socket, operating the switch should give you open circuit (if polarity is correct)

Anyone shed a bit more light? I might have missed the obvious here but bear in mind I've been revising for hours

​My red
 
typical ambiguous question. as the Q. says continuity test, rather than end/end, i would assume it meant R1+R2, which, as jud said, would confirm both polarity and cont. of cpc.
 
The Question and answer were stated in IEE city and guilds 2391 exam success book

The wording is really stupid, why doesn't isn't ask " a ring final circuit r1 + r2 continuity test is to be carried out, state two additional tests automatically carried out when doing this test


I wonder how many people got that correct when it was put on a real paper, I can't imagine many, its only when you analyse the question with others that it becomes more clear
 
What I don't understand, is how confirmation of continuity of the CPC can be considered as additional, when you are conducting a continuity test?
 
Yes that was my point "spinlondon" how can something be additional when carrying it out initially

On a exam after reading that question how many people do you think wrote "continuity of Cpcs"?
 
No problem with Polarity.

The only thing I can think of to explain answer 'b' is that the end to end tests will yield a result for R2 alone (r2/4).
Hardly automatic though, seeing as you've already measured and recorded the r2 value!

I'd have said the tests would show up any interconnections, but the question says 'new installation', so you you wouldn't expect any.


Horrible question. I wouldn't give it 5 seconds if I saw that in the exam. Leave a gap and move on, it's only 1 mark (I assume).
 