Hi all will try to be straight to point !
large house 3 ph supply to 3 ph CU, meter box outside previous spark has henley blocked off yellow phase to seperate isolator(in meter box)SWA (25mm) to granny flat 1 x bed 1 x bath kitchenette sod all Load!.they are converting another outbuilding into 3 garages and flat/bedsit above! My thoughts are to take 10mm SWA from 50a 60898 in Granny flat to seperate CU in Garages, I would appreciate any comments/ideas/criticisms on this ! cheers in advance
 
Is there not a spare way on the 3 phase board, would look better than coming off of the granny board?
 
Does sound like it would be better from the main board rather than granny flat...

From whats described...
 
im gonna buck the trend and say tap off the nearest lampost , let the dno worry about balancing their own god damn phases.
;-)
 
Hi all will try to be straight to point !
large house 3 ph supply to 3 ph CU, meter box outside previous spark has henley blocked off yellow phase to seperate isolator(in meter box)SWA (25mm) to granny flat 1 x bed 1 x bath kitchenette sod all Load!.they are converting another outbuilding into 3 garages and flat/bedsit above! My thoughts are to take 10mm SWA from 50a 60898 in Granny flat to seperate CU in Garages, I would appreciate any comments/ideas/criticisms on this ! cheers in advance


I hope that's a switch fuse and not just an isolator??
That 25mm SWA, may be compensating for the length of run rather than the connected load!! lol!! But it does sound to be a little OTT...lol!!
 