Hi guys, we have a 3 phase 415V 36kw furnace. Just wanted to know the fuse needed for each phase. we put a 40A fuse for each phase and 1 phase just blew when started firing it up. I tried to calculate the right fuse and I come up with 65A per phase? Is that right?
 
Hi guys, we have a 3 phase 415V 36kw furnace. Just wanted to know the fuse needed for each phase. we put a 40A fuse for each phase and 1 phase just blew when started firing it up. I tried to calculate the right fuse and I come up with 65A per phase? Is that right?
MJ if I’m right and help me out 3 phase calculations is 415x1.73=719.9 36,000 divided by 719=50 amps since you are using a fuse 50x 1.75 = 87 is this the way y’all do your calculations?
[automerge]1567730867[/automerge]
MJ if I’m right and help me out 3 phase calculations is 415x1.73=719.9 36,000 divided by 719=50 amps since you are using a fuse 50x 1.75 = 87 is this the way y’all do your calculations?
That’s the USA calculations
 
MJ if I’m right and help me out 3 phase calculations is 415x1.73=719.9 36,000 divided by 719=50 amps since you are using a fuse 50x 1.75 = 87 is this the way y’all do your calculations?
Hi megawatt, What I did was 36000/3 = 12000VA per phase, 12000/240 = 50 x 1.25 = 62.5A per phase. Where 240 is line to neutral 415/1.732=240. does that make sense?
[automerge]1567733017[/automerge]
MJ if I’m right and help me out 3 phase calculations is 415x1.73=719.9 36,000 divided by 719=50 amps since you are using a fuse 50x 1.75 = 87 is this the way y’all do your calculations?
[automerge]1567730867[/automerge]

That’s the USA calculations
I see, interesting...
[automerge]1567733131[/automerge]
MJ if I’m right and help me out 3 phase calculations is 415x1.73=719.9 36,000 divided by 719=50 amps since you are using a fuse 50x 1.75 = 87 is this the way y’all do your calculations?
[automerge]1567730867[/automerge]

That’s the USA calculations
Where'd you get that 1.75? 175% of rated current since i'm using a fuse?
 
Hi megawatt, What I did was 36000/3 = 12000VA per phase, 12000/240 = 50 x 1.25 = 62.5A per phase. Where 240 is line to neutral 415/1.732=240. does that make sense?
[automerge]1567733017[/automerge]

I see, interesting...
[automerge]1567733131[/automerge]

Where'd you get that 1.75? 175% of rated current since i'm using a fuse?
In the USA we use a chart for your overcurrent protection fuse are 1.75% if you are using inverse time breakers you can use 2.25%
[automerge]1567734155[/automerge]
In the USA we use a chart for your overcurrent protection fuse are 1.75% if you are using inverse time breakers you can use 2.25%
If it started for you I would leave it there it’s just inrush current you have to get through
[automerge]1567734385[/automerge]
In the USA we use a chart for your overcurrent protection fuse are 1.75% if you are using inverse time breakers you can use 2.25%
[automerge]1567734155[/automerge]

If it started for you I would leave it there it’s just inrush current you have to get through
I guess different ways of doing things but as long as we get it running
 
Last edited:
Q.1. what size cable is feeding this furnace? this will determine the size of fuse, as long as it's ccc is > the load current.
Q.2. have you dead tested the furnace to ensure that there are no faults, esp on the phase that blew the fuse. ?

for that load i would expect a 10mm cable.
 
36,000 / (400x1.732) = 51.96A. This is your design current (Ib)

Select a fuse rating (In) that suits your (Ib) and make sure the tabulated ccc (It) of your supply cable is greater than (In) after any correction factors have been applied.
 
I would advise you to use suitable calculators. You can find many free ones on the net. For example:

3 phase furnace 1567779374483 - EletriciansForums.net
Power factor = 1.0

Design current = 50A,

Protection = fuse gG 63A, or MCB C63A

Note that the furnace has a short starting current while the heating elements are still cold.
 

Reply to 3 phase furnace in the Industrial Electrician Talk area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock