Working on an empty property which has 4 RFCs. 3 of these are showing no continuity across R1 R2 and Rn. The wiring is around 30 years old and each room has 2/3 single sockets. Each of these sockets is fed by a single 2.5mm T&E. What's going on here? Is it likely the sockets are being fed from a ring under the floor with a junction and spur for each socket? This could give plausibility for their being a break in one of the junctions but it just doesn't make sense. I'm heading back tomorrow to investigate properly but keen to know if anyone has come across similar before?
 
You say 4 RFC's and 3 have no continuity on r1, rn, and r2........and there is a single 2.5 T/E at each socket. Well in that case the three are clearly not RFC's!
Assuming other tests are satisfactory if you are there to alter these circuits treat them as 20a radials, or if they need a 32a OCPD they will have to be rewired as rings.
 
If you have 2 cables at the fuse board but only 1 at the sockets then at some point someone has split the ring under the floor most likely in a JB

not a particulary big issue and most likely been like this for years
 
Can you tell with the age of the sockets themselves? Ie 30 year old, splash painted the same colour as the wall will be original on rfc... anything new, or doesn’t match might be additions.
Also listen out for squeaky floorboards.... hint that they have been lifted.... that could be where the joints are.
 
Presumably the end to end testing was done at the DB if you only have single cables feeding at the sockets? Looks like you'll have to test for continuity for each socket back to the one leg to try and make sense of the arrangement or start pulling floorboards up. Sounds like you may be right about an RFC with the sockets dropped off in spurs which I've come across a few times but you should still get an end to end reading at the DB.
 
Can you tell with the age of the sockets themselves? Ie 30 year old, splash painted the same colour as the wall will be original on rfc... anything new, or doesn’t match might be additions.
Also listen out for squeaky floorboards.... hint that they have been lifted.... that could be where the joints are.
Sockets appear to be same age as the wiring. 30 years. Hence I’m slightly confused. No evidence of DIY.
 
Just realised, 30 years old, it's a Ring Main not a Final Ring Circuit, Ring Mains flow from right too left instead of from Left too Right, to bring them in line with the rotation of the Earth they where changed to Final Ring Circuits, unless anyone knows of some other reason. ??
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
3 x RFC all with no continuity
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
20
Unsolved
--

Advert

Thread statistics

Created
JosephandAmber,
Last reply from
westward10,
Replies
20
Views
3,112

Advert

Back
Top