P

pcam1984

Sent to a job today, testing been done by another company and remedial works sent to us. Flagged up that a 3ph supply for kitchen fryer is wired using 2 t+e cables, i had to run in 4c swa. On opening the db found that there are 3 circuits wired like this. Any suggestions as to why the testing guy would only pick up one. It was a 20% test but blatantly obvious as soon as you open board, maybe he only spotted it at other end and hasn't opened db.
 
I thought it was required to test all circuits and that 20% referred to taking off faceplates, covers etc.........
 
Poor tester imo on any test if you find anything wrong you should always go a bit further,maybe he found the 1st one by accident.
 
We've been told that as the premises require 100% every 5 years if they test 20% of installation every year this equals 100% every 5
 
Whichever way you look it's a poor inspection,a good look at the board should have shown him they'd used t&e.some people either don't know or don't care how they do a job.
 
We've been told that as the premises require 100% every 5 years if they test 20% of installation every year this equals 100% every 5

That only could work if the same person does the tests each year!

No wonder some companies pay so little for their testing!
 
We've been told that as the premises require 100% every 5 years if they test 20% of installation every year this equals 100% every 5

That's true but the amount of companies I see getting this wrong is untrue. Only doing 20% every 5 year's, usually just going round taking Zs. I see the certificates full of LIM.
 
Not sure why anyone would not look in the board tbh?
That would be the first thing I look at in any scenario.

I was told when I was a mere apprentice that you can tell alot about a system and the people who wired it by the board.
If its neat and tidy, labeled etc the guy has pride and you would have to look hard for something wrong.
If its a mess, wrong labels/colors etc etc expect big problems!

Obviously this is not always 100% correct but usually a good indicator.
 