Hi all, just to further my last post re supply to flats from an old pub.
If the pub is supplied by 100a 3ph then I could easily supply 3 of the flats.
Working on maximum demand per flat of:-
Flat ring 32a
Kitchen ring 32a
Lighting circuits 12a
Boiler 3a
Air con 10a
Total of 89a but we all know the flat will never be at full demand, was going to say 60A to be on safe side?
Could I utilise the other phases to gain the 4th 60a supply??
Also how would you install this? I assume where the intake point is you would have to make that into a little sub room? Would you put the meters for the flats in the sub room then run a armoured to supply consumer unit for each flat?
Could I move existing supply if in the way?
Any advice or guidance would be great lads
Cheers