S

Sparky28

Hi all, just to further my last post re supply to flats from an old pub.

If the pub is supplied by 100a 3ph then I could easily supply 3 of the flats.

Working on maximum demand per flat of:-
Flat ring 32a
Kitchen ring 32a
Lighting circuits 12a
Boiler 3a
Air con 10a

Total of 89a but we all know the flat will never be at full demand, was going to say 60A to be on safe side?

Could I utilise the other phases to gain the 4th 60a supply??

Also how would you install this? I assume where the intake point is you would have to make that into a little sub room? Would you put the meters for the flats in the sub room then run a armoured to supply consumer unit for each flat?

Could I move existing supply if in the way?

Any advice or guidance would be great lads :)

Cheers
 
3 phases & 4 flats = 2 of the flats sharing 1 of the phases.
wont be a problem though , massive diversities can be applied for buildings of multiple occupancy.
have all of the meters located together near the intake supply to make meter reading easier and then feed each of the flats with a bs88 63A switchfuse.
happy days.
 
The incoming supply is more than adequate for 4 flats. Like you said factoring in diversity for the flats will mean your unlikely to see anyone pulling 60 amps to be honest. Even less likely any two flats would be drawing that current at the same time! No electric showers? electric cookers? You will also need to do a landlords supply for common hallways I imagine?? I would be coming out of the Henley blocks in the entrance hall cupboard with tails into Wylex metal clad boxes, with 60amp cartridge fuse per flat. SWA cables out of the box, size is big enough for you to work in that type of enclosure comfortably with the glands etc...........SWA to each Flat consumer unit. What about kwh meter's? Is each flat to be on it's independent meter or has the landlord included utilities in their rental prices?? I think your only real concern is trying to balance the three phases as best you can, but even that goes out of the window if one of flats is unoccupied. No doubt more experienced sparks will have a different take to me, but I would not panic about your incoming supply size.
 
Cheers chaps :))
No electric cooker or showers, just to keep load down really. Gas cooker and mixer shower the way forward :))
 